    Having trouble with an ac unit, need help!!
    Jan 2011
    TN
    more info
    Aug 2011
    Head pressure does not move off of 150, comp runs for bout a min, suction drops to 50, internal overload takes it out
    this thing got a model #
    you sure the hoses are working?
    does this thing have service valves?
    Aug 2011
    model ckl-120-3l
    brand new set of hoses and manifold
    it does have valves, thats how i read the pressures
    Oct 2008
    Nashville ,TN
    sure its OL and not low pressure switch?
    Tallahassee, FL
    Amp draw?
    Apr 2009
    San Diego
    internal overload is usually caused by compressor getting too hot and that takes longer than 1 minute. Your low pressure switch will cause unit to shutdown as you explained. Quick way to check that is check for 24 volts across the low pressure switch. It will be 0 if all is good. It will be 24V it the low pressure switch opens. of course you will see 0 until the unit shuts down and the contactor plunger pops out then at the exact same time you will see 24 V at your meter.
    Aug 2011
    Contractor stays in and the fan stays running, company terminals shows open, its a fixed orifice system, could the problem be there?