Thread: Tapping Coming From Primary Condensate Line

  1. #1
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes

    Tapping Coming From Primary Condensate Line

    It's a steady tapping or knocking sound. I removed the side cover from the air handler while it was running and the blower seems fine. No bearing problems or other noticable issues. If I completely plug the end of the condensate line, the sound disappears. Any ideas on what the noise source might be?

  2. #2
    Join Date
    Apr 2010
    Location
    SC
    Posts
    34
    Post Likes

    Drain Trap

    Sounds like you dont have condensate trap or the trap is not correctly installed. What type of A/H do you have, model number and make might help.

  3. #3
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes
    Thread Starter
    Thanks for the response elroho. I bought the house last summer, the airhandler is older. I'll need to get back in the attic tonight to get the info.

  4. #4
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes
    Thread Starter
    I don't remember seeing a trap up there. Do these EZTraps work?http://www.hvacsolutionsdirect.com/i...files/1711.pdf

  5. #5
    Join Date
    Apr 2009
    Location
    San Diego
    Posts
    75
    Post Likes
    its called air hammering and a trap and tee after the trap will fix the sound

  6. #6
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes
    Thread Starter
    By tee, I assume you mean a vent? I'm on it. Lowes here I come.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Haryy Homeowner View Post
    By tee, I assume you mean a vent? I'm on it. Lowes here I come.
    Before you go chopping up your drain line and creating more problems than you solve, two traps in one line is not a good idea.

    The first thing I think of is vibration. A few ty wraps or clamps would solve that problem. Putting your hand over the end has the effect of securing the line temporarily.

    The next thing would be excessive air pressure causing bubbling or gurgling through the trap. This indicates the need for a professional to properly diagnose and remedy the problem.



  8. #8
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes
    Thread Starter
    Thanks so much. This is all very helpful guys.
    I can say that the problem is not from vibration. That's what I had originally hoped was the cause. I've checked for that.
    I guess it's possible that my unit has an internal trap. I'll have tio figure out how to access that section of the unit.
    Would excessive preesure cause air to be blowing out of the condensate drain line?
    Can I test for excessive pressure by simply opening up the duct on the discharge of the blower and if the tapping stops, I'll know that's the problem?

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Haryy Homeowner View Post
    Thanks so much. This is all very helpful guys.
    I can say that the problem is not from vibration. That's what I had originally hoped was the cause. I've checked for that.
    I guess it's possible that my unit has an internal trap. I'll have tio figure out how to access that section of the unit.
    Would excessive preesure cause air to be blowing out of the condensate drain line?
    Can I test for excessive pressure by simply opening up the duct on the discharge of the blower and if the tapping stops, I'll know that's the problem?
    A single trap is all that is required in a drain.

    Testing for air pressure requires a manometer.



  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by C Combs View Post
    its called air hammering and a trap and tee after the trap will fix the sound
    C Combs,

    Please read the AOP forum rules.

    You have the post count, so apply for Professional Membership to gain access to the Technical Forums.



  11. #11
    Join Date
    Aug 2011
    Location
    Virginia
    Posts
    6
    Post Likes
    Thread Starter
    There was no trap in the condensate drain line. I installed a trap and vent and the knocking 's gone. Thanks.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •