Thread: Heat Pump - Won't Stay On - Urgent

  1. #1
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    I have a medical condition that cannot tolerate cold and am desperate.

    We have just moved into our new home. Something is wrong with the heat pump and I cannot get the service/warranty people out here till Monday.

    When the thermostat is set for heat there is air blowing, but it is not hot. It takes about 2 hours to go up one degree. The outside unit meanwhile (It is a Bryant system) is running about 30 seconds, tuns off, then starts again - this is continuous when the heat is turned on. It did appear prior to close whenever we were in the house that the cooling part of this heat pump was functioning, but maybe it just wasn't that hot.

    Does anyone recognize this problem as being something caused by a simple/stupid glitch somewhere we can possibly do something about today? We have checked the filter to make sure it's not clogged by contruction debris so far, it is clean.




  2. #2
    Join Date
    Jan 2004
    Location
    Location: Tulsa Oklahoma
    Posts
    222
    Post Likes
    I would look in the phone book for a service company that works on the weekend and pay them to come check out your problem.

  3. #3
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    if you have auxilliary heat, turn the thermostat switch to emergency heat until the service co. can get there. do not keep running the outdoor unit in this condition.

    good luck.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Switch the stat to EMG, and wait for the installing contractor.

  5. #5
    Join Date
    Mar 2001
    Posts
    288
    Post Likes

    Switch your thermostat to "EM heat" Aux heat or Supl heat....do not allow the outdoor unit to run in this condition....get a weekend svc company or wait until monday

  6. #6
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter
    Wow - thanks for all the responses! So, there seems to be a consensus here, but I have always been confused about this Emergency Heat setting.

    Apparently the Emergency Heat setting does not involve the outdoor unit at all? Am I getting that right? Is this the same thing as Auxillary Heat or not?

    Okay - I have made the switch, but so far it seems the system is not kicking in at all on this setting.

    By the way - this setting is gonna cost me a fortune on the electric end isn't it? Might as well pay someone to get out here anyway - still trying to find someone.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    May have multiple wiring issues.

    Yes it will run up the electric for the day if the strips are working.

    If you use a different contractor then the installer, you could run in to trouble down the road if some thing else goes wrong.

    It could end up in a P match between the 2 contractors blaming each other.

  8. #8
    Join Date
    Oct 2002
    Location
    Yo.... Here!, I'm right here..
    Posts
    6,231
    Post Likes
    I'll second beenthere's response
    and it won't cost all that much to run the backup heat for one day,

    builders contractors sometimes don't do or aren't very good at service

  9. #9
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    Originally posted by relentless


    Okay - I have made the switch, but so far it seems the system is not kicking in at all on this setting.

    By the way - this setting is gonna cost me a fortune on the electric end isn't it? Might as well pay someone to get out here anyway - still trying to find someone.
    Did you make sure the stat was also set in the heat mode with the emg. heat switch on?

    It is better to have to pay a little cash out for electric for one day than to freeze.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  10. #10
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter
    Oh, good point beenthere - thanks for reminding me. I don't want to end up voiding the warranty if the unit needs replacement - yikes.

    Okay, I have also turned on the fan since it wasn't kicking in on EHEAT setting hoping to get the air flowing. Any problem with that?

  11. #11
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter
    Originally posted by davidr

    Did you make sure the stat was also set in the heat mode with the emg. heat switch on?

    It is better to have to pay a little cash out for electric for one day than to freeze. [/B]
    Agreed about the money - but the stat is how you turn it to emg heat. Is there something somewhere else I need to flip?

  12. #12
    Join Date
    Aug 2002
    Posts
    255
    Post Likes
    Originally posted by beenthere
    May have multiple wiring issues.

    Yes it will run up the electric for the day if the strips are working.

    If you use a different contractor then the installer, you could run in to trouble down the road if some thing else goes wrong.

    It could end up in a P match between the 2 contractors blaming each other.
    how many people here install units and then tell homeowner "i'll see ya Monday "if they have problem, i would call contractor number 2 any how.They should service what they sell on 24 hour call at least explain to customer how to set emergency heat.

  13. #13
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    Originally posted by relentless


    Agreed about the money - but the stat is how you turn it to emg heat. Is there something somewhere else I need to flip?
    Just make sure it is set to heat in addition to emg.heat.
    I just had this same issue with a customer last week.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  14. #14
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter

    Frown

    Okay - It is set to heat/emergency heat, I've cranked the requested temp 6 degrees above the thermostat reading and the system isn't running at all. Tried setting the fan to stay on and that didn't help. Actually, if I turn it on (the fan) for a bit, then turn it off, the system stays running on it's own for about another 5 minutes, but not long enough to go up a degree.

    So I guess I have no emergency heat on the thing either. The thermostat shows it is on, the system just doesn't run in this mode. I mean it should be blowing something in this mode right? Grrrrrrrrr.

  15. #15
    Join Date
    Oct 2002
    Location
    Yo.... Here!, I'm right here..
    Posts
    6,231
    Post Likes

    On the thermostat

    Set the system to off and the fan to on,,wait 1 minute anything? happen ??

    you should have a blower running.

    yes or no

    [Edited by pjs on 12-04-2005 at 01:16 PM]

  16. #16
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter
    Yes - the fan works fine all by itself. (With the thermostat off even)

  17. #17
    Join Date
    Oct 2002
    Location
    Yo.... Here!, I'm right here..
    Posts
    6,231
    Post Likes
    Is there a double breaker on the front of the air handler

  18. #18
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    3,097
    Post Likes
    Originally posted by relentless
    Okay - It is set to heat/emergency heat, I've cranked the requested temp 6 degrees above the thermostat reading and the system isn't running at all. Tried setting the fan to stay on and that didn't help. Actually, if I turn it on (the fan) for a bit, then turn it off, the system stays running on it's own for about another 5 minutes, but not long enough to go up a degree.

    So I guess I have no emergency heat on the thing either. The thermostat shows it is on, the system just doesn't run in this mode. I mean it should be blowing something in this mode right? Grrrrrrrrr.
    Sounds like you have a wiring issue with the emergency heat, or it is like many I see around here and just does not have enough Kw to make a difference without the heat pump running. It is very commom here to see the emergency heat not wired up and we also see only 5 kw strips fairly often. Really just useless when you really need heat.

    Bobby

  19. #19
    Join Date
    Dec 2005
    Posts
    8
    Post Likes
    Thread Starter
    Okay - we have heat. A guy came by and it there was something (a valve loose) so all the fluid had been leaking out.

    But yes, you are correct regarding the emergency heat. It is definately not wired or miswired, so I am glad to have discovered this now. I will still call the builder to get that corrected, but at least I can sleep here tonight.

    You guys are great and I am overwhelmed by the amount of assistance offered.

    THANK YOU!

  20. #20
    Join Date
    Oct 2002
    Location
    Yo.... Here!, I'm right here..
    Posts
    6,231
    Post Likes
    Your Welcome

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •