Head skyrockets and low drops...IN SECS!
On start up, head pressure sky rockets past 450 in secs, and low side drops below 10 at the same speed. On shut off , they take forever to equalize...actually i didnt stay there long enough to see if it even would.
Wheres the most likely plug? Txv system , carrier water cooled 10 ton package unit r22.“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
08-30-2011, 02:28 PM #2
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
i think you hit it with the txv or plugged screen but also sounds like it could
be over charged with the head going up like that.
-
08-30-2011, 02:36 PM #3
Does it have a solinoid valve in the liquid line?
Nemo me impune lacessit.
How much blood do I have to bathe in to get clean?
Don't look down on anyone unless you're helping them up.
-
08-30-2011, 02:39 PM #4
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
Found it. Stuck close TXV. Noticed no cold at outlet. I counted turns one way and when i hit about 4 full turns, I heard it screamin through and got cold, and equalized the system right away.
“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
08-30-2011, 08:25 PM #5
Professional Member
- Join Date
- Apr 2006
- Location
- mechanical room
- Posts
- 1,212
i've never seen a stuck txv cause the head to go up like that, was it overcharged ?
-
08-30-2011, 10:08 PM #6
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
I just got back into the plant 10 min ago.
No i cant be overcharged. I mean I didnt pull the charge, and the system has been runnin AS IS for 3 yrs. Meaning, no opening up of system.
I think its IN FACT UNDERCHARGED...baby leak from shraeder valve when I took cap off....Maybe just slightly....but definatley NOT OVER.
I'll get some readings and temps and get back in a few. Hope you all keep up wit me on this.“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
08-30-2011, 10:12 PM #7
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
08-30-2011, 10:25 PM #8
Professional Member
- Join Date
- Apr 2006
- Location
- mechanical room
- Posts
- 1,212
oh yeah ur right the water cooled condensers are much smaller and hold alot less refrigerant, causing the refrierant to stack up into the discharge side and contributes to the high press.