    On start up, head pressure sky rockets past 450 in secs, and low side drops below 10 at the same speed. On shut off , they take forever to equalize...actually i didnt stay there long enough to see if it even would.
    Wheres the most likely plug? Txv system , carrier water cooled 10 ton package unit r22.
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
    I'm learning all the time, the tombstone will be my diploma!!!
    Did you ever stop to think, and forget to start again?
    las vegas
    i think you hit it with the txv or plugged screen but also sounds like it could
    be over charged with the head going up like that.
    Oct 2007
    Austin Texas
    Does it have a solinoid valve in the liquid line?
    Nemo me impune lacessit.
    How much blood do I have to bathe in to get clean?
    Don't look down on anyone unless you're helping them up.
    New Jersey
    Found it. Stuck close TXV. Noticed no cold at outlet. I counted turns one way and when i hit about 4 full turns, I heard it screamin through and got cold, and equalized the system right away.
    Apr 2006
    mechanical room
    i've never seen a stuck txv cause the head to go up like that, was it overcharged ?
    New Jersey
    Quote Originally Posted by coolerinfrederick View Post
    I just got back into the plant 10 min ago.
    No i cant be overcharged. I mean I didnt pull the charge, and the system has been runnin AS IS for 3 yrs. Meaning, no opening up of system.
    I think its IN FACT UNDERCHARGED...baby leak from shraeder valve when I took cap off....Maybe just slightly....but definatley NOT OVER.
    I'll get some readings and temps and get back in a few. Hope you all keep up wit me on this.
    New Jersey
    I also heard that due to the fact that its water cooled..makin it more efficient...gives it less condenser room, gives it less time and room to stack up in the high side........
    Does this contribute? and how? if so or not?
    Apr 2006
    mechanical room
    oh yeah ur right the water cooled condensers are much smaller and hold alot less refrigerant, causing the refrierant to stack up into the discharge side and contributes to the high press.