08-10-2011, 05:10 PM #1
Regular Guest
- Join Date
- Jan 2010
- Location
- Van Buren Arkansas
- Posts
- 16
Wire size
I came across a 5 ton Rheem condenser the other day, with a 50 amp min. circuit capacity. It had a 30 amp breaker at the panel. The customer has called the electrician. When they are done., I am going back to resize the wire from the disconnect to the condenser. It is currently running a 10 wire. I'm thinking; at least 8 AWG.
-
08-10-2011, 05:38 PM #2
banned reincarnate
- Join Date
- Aug 2011
- Posts
- 568
-
08-10-2011, 07:31 PM #3
Regular Guest
- Join Date
- Jan 2010
- Location
- Van Buren Arkansas
- Posts
- 16
wire size
MM#7, my understanding is the electrician only goes to the disconnect, from the breaker panel, and HVAC, goes from the disconnect to the unit; and, since the unit is a 5 ton, and is only, using a 10 AWG wire, I was considering rewiring with at least 8 AWG.
-
08-10-2011, 07:37 PM #4
banned reincarnate
- Join Date
- Aug 2011
- Posts
- 568
-
08-10-2011, 07:41 PM #5
-
08-10-2011, 07:43 PM #6
banned reincarnate
- Join Date
- Aug 2011
- Posts
- 568
-
08-10-2011, 08:05 PM #7
Professional Member
- Join Date
- Mar 2011
- Location
- far southwest chicago suburbs
- Posts
- 133
If this is a union job, electricians wire all the way, if its not, let the electrician wire it all the way. Or use the same size he runs to the disconnect.
-
08-10-2011, 10:39 PM #8
Regular Guest
- Join Date
- Jan 2010
- Location
- Van Buren Arkansas
- Posts
- 16
-
08-10-2011, 11:22 PM #9
banned reincarnate
- Join Date
- Aug 2011
- Posts
- 568
-
08-11-2011, 06:46 AM #10
Professional Member*
- Join Date
- Aug 2008
- Location
- S. Grand Prairie
- Posts
- 243
I'd either let the electrician do the wiring as mentioned above...or, since your not sure of the correct gauge wire, ask him when he's there...
Originally Posted by ladyfire3374:
"I used to wake up excited about the challenges of the day. Now the anticipation level is somewhere between a root canal and a colonoscopy."
-
08-11-2011, 06:54 AM #11
Professional Member
- Join Date
- Nov 2006
- Location
- 801 Del Rio pike Franklin Tennessee
- Posts
- 119
Run two 6awg and one 8awg ground. on a 50 amp. cya.
-
08-11-2011, 07:17 AM #12
In Ontario, Canada the Hvac tech can wire from the panel (including installation of the breaker) to the ac condenser unit, provided he has a refrigeration license, follows the code and gets an inspection....
Never give up; Never surrender!
-
08-11-2011, 07:34 AM #13[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules: