    Trane XL16i - fuse blowing on ouside unit

    I have a Trane XL16i. The outside unit is a 4TWX6036C1000AA. It has a 5 amp ATO fuse in the low voltage control circuit that blew last night. The fan runs, but the compressor won't. The Tech came out and replaced it, it blew again. He could not figure it out and is waiting for the main tech to get back tonight and will try again tomorrow.

    Based on the diagram this fuse is inline with the red wire from the 24 volt transformer on the outside unit and goes to the main circuit board connector J1.

    Any ideas?

  2. #2
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    520
    Tell him to ohm out the contactor coil, reversing valve coil, inspect the control board for shorts. Is it set up as a communicating system? Must be, since you have a fuse in the outdoor unit.

  3. #3
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    BTW, I believe the Tech questioned why a 24V transformer outside and one inside. If he disconnected the inside the fuse would not blow and wondered if the orginal installers wired it correctly. My question to him was it came from the factory like that and worked Ok for almost 3 years. What changed last night to blow the fuse?

  4. #4
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    520
    What's it paired up with inside? The outside transformer powers the outdoor board and all outdoor functions. The outdoor communicates to the indoor unit via 2 wires.

    If it has the standard 6 wire pigtail at the outdoor unit, then the outdoor transformer should not even be hooked up.

  5. #5
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    Quote Originally Posted by dunkman View Post
    Tell him to ohm out the contactor coil, reversing valve coil, inspect the control board for shorts. Is it set up as a communicating system? Must be, since you have a fuse in the outdoor unit.
    I wish I had the correct answere on that. Don't know if it is a communicating system or not. There is no place for a readout. There is one green led on the outside unit that is flashing a rapid burst but the tech has nothing to read it with.

  6. #6
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    520
    2 wires=communicating

    6 wires=non-communicating, and the outdoor transformer should not even be hooked up.

  7. #7
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    Quote Originally Posted by dunkman View Post
    What's it paired up with inside? The outside transformer powers the outdoor board and all outdoor functions. The outdoor communicates to the indoor unit via 2 wires.

    If it has the standard 6 wire pigtail at the outdoor unit, then the outdoor transformer should not even be hooked up.
    Inside unit is a 4TEE3F40B1000AA
    Outside unit is a 4TWX6036C1000AA
    Honeywell Zone controller HZ322
    3 Trane XR402 "thermostats" feed the honeywell.

    It is using the 6 wire pigtail to control the outside unit. I am assuming it cannot use a 2 wire setup due to the Zone system???

  8. #8
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    Quote Originally Posted by dunkman View Post
    2 wires=communicating

    6 wires=non-communicating, and the outdoor transformer should not even be hooked up.
    Well that may be why the fuse blew. It probly blew 3 years ago and no one noticed until this problem came up and noticed the fuse had popped.

    The orginal installer really had a time making it work. The carpenders told me he was on the phone with someone getting directions on how to hook it all up.

    I orginally asked for a 2 ton XL16i system for the first floor and was going to install small split units in each bedroon on the second floor. The contractor and Trane installer talked me into going with a 3 zone system instead. 1st, floor, 2nd floor, den(in basement).

  9. #9
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    520
    These two threads should be merged together. http://hvac-talk.com/vbb/showthread.php?t=912682

    The zone system is not a "communicating system". That heat pump comes out of the box as "communicating." Whoever installed the wiring kit to make it non-communicating did not remove the wires from the outdoor transformer. I don't know how the heck it made it 3 years without issue. Sounds like the original installer messed this whole thing up. If your tech isn't familiar with the 16i he needs to get a copy of the instructions for the "non communicating low voltage harness" I can't remember the part # off the top of my head. We quit using them a few months ago.

  10. #10
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    Quote Originally Posted by dunkman View Post
    These two threads should be merged together. http://hvac-talk.com/vbb/showthread.php?t=912682

    The zone system is not a "communicating system". That heat pump comes out of the box as "communicating." Whoever installed the wiring kit to make it non-communicating did not remove the wires from the outdoor transformer. I don't know how the heck it made it 3 years without issue. Sounds like the original installer messed this whole thing up. If your tech isn't familiar with the 16i he needs to get a copy of the instructions for the "non communicating low voltage harness" I can't remember the part # off the top of my head. We quit using them a few months ago.
    Dunkman
    Thanks for the suggestion, butI did not put them together because the 2 questions were not related and it has been my experience when you discuss 2 different issues thing get confused. I do have a addition to the other thread having just talked with Honeywell.

  11. #11
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by dunkman View Post
    These two threads should be merged together. http://hvac-talk.com/vbb/showthread.php?t=912682

    The zone system is not a "communicating system". That heat pump comes out of the box as "communicating." Whoever installed the wiring kit to make it non-communicating did not remove the wires from the outdoor transformer. I don't know how the heck it made it 3 years without issue. Sounds like the original installer messed this whole thing up. If your tech isn't familiar with the 16i he needs to get a copy of the instructions for the "non communicating low voltage harness" I can't remember the part # off the top of my head. We quit using them a few months ago.
    BAYACHP024A WIRING HARNESS

  12. #12
    Join Date
    Dec 2008
    Location
    Northeast Tennessee
    Posts
    50
    Quote Originally Posted by second opinion View Post
    BAYACHP024A WIRING HARNESS
    Would this, the harness, still apply in a Zone system?

  13. #13
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    520
    Quote Originally Posted by navyjoe View Post
    Would this, the harness, still apply in a Zone system?
    absolutely.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event