Results 27 to 34 of 34
09-18-2011, 01:14 PM #27
It doesn't matter that the service port is after the valve. I have pumped systems down with a solenoid valve leaving the service port open the gauge. I didn't believe my teacher when he said a restriction wouldn't cause a high head pressure so I did it and the head pressure did not go up.
I agree
I also agree, and I am not intending to be rude but I did put a PS disclaimer to note that what I posted was not always the case. Please don't think I am stepping on any toes because I know I don't know everything and I learn a lot just lurking around here.
09-18-2011, 03:04 PM #28
I am sorry but I still stand by the physics of it , If a line some thing goes thru is stopped up no matter where it is in the system is going to cause some type of adverse/unwanted operating condition and pressure changes . I am one of those have to see to believe it guys and the pumpdown test just does not make sense to me. A hot gas valve for instance if I am not mistaken traps a small amount of hot gas out of the compressor before it goes into the condenser and stores it behind the H/G valve and then the gas is used during the defrost cycle of ice machines and other types of refrigeration applications. My point is that we are creating a little electrically controlled mini restriction and using it to our advantaged ,but it is controlled and planned and therefore does not create any adverse or unwanted operating conditions. Which IMO an uncontrolled line restriction is going to cause some type of pressure change somewhere in the system. I realize that refrigerant is a strange beast sometimes especailly in large quantities or in elaborate piping schemes where it changes state many times . But physical space is physical space and only so much any thing can fit in a predetermined space . Also I wanna say that I do NOT know it all ,I just think simple things should be kept simple. I am always willing to learn new things and feel like knowledge is the best tool any tech can have. Sorry if I sound"that way" I just feel like right is right and when there is an equation that does not have variables ,there should be none added for the sake of conversation.
"I just think things should work properly"
Freon is a brand name-word
09-18-2011, 03:15 PM #29
09-18-2011, 10:13 PM #30
- Mar 2011
- Parker, Colorado
- 25
09-18-2011, 11:03 PM #31
You need to take basic steps before you go taking the refrigerant out and changing the TEV. Subcooling would have been the first route to take . 4 years old and no problems till this summer. You know that the ductwork is probably fine. Was the filter ok? Check the a-coil. I am assuming your standing pressure test passed before you continued on with your vacuum? Should have changed your filter drier since you opened the system up. If you tested your TEV then you would already know it wasn't it. Let us know what your subcooling is.
If your not getting the results you desire then change. People change from either desperation or inspiration.
09-18-2011, 11:11 PM #32
- Sep 2008
- Cedar Rapids, IA
- 473
Line temp 50 and pressure 50# is about 25 degree superheat. If subcooling is good then the problem is TXV or its adjustment. Assuming the measurements were made at the evap coil it doesn't look like an air flow problem. If low subcooling then its a low charge problem.
09-19-2011, 08:30 AM #33
09-19-2011, 11:25 AM #34
- Jul 2007
- New Jersey
- 3,031
It doesnt matter what the dry bulb is indoor or outdoor for the coil to freeze. As soon as you said 180 head and 50 suction, my first "guess" was low charge. 50 sat temp is 25-26 = below freezing.
Any moisture, humidity or condensate is gonna freeze on that coil. And unless the tstat satisfies and the fan stays in ON, its gonna keep freezing and spreading.
You head is also too low for an 80° day. I would like to see in the 230 - 260 range. But anything under 200psig for R22 head pressure, either theres an issue, or the darn thing shouldnt even be running.
But no ideas count with limited info giving. SH/SC is a must for this type of question.
Good Luck“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?