    Question TEV Equilizer tube size

    I was purchasing a replacement TEV for a 2.5 ton heat pump and the old equalizer was 1/4" and the new one was small 1/8" I believe. I stubbed it down in the old 1/4" tube and crimped it nice and pretty and brazed them up. The unit runs fine, so does equalizer tube size really matter at all?

  2. #2
    Join Date
    Aug 2011
    Location
    Goose Creek ,SC
    Posts
    252
    just realized I spelled equalizer wrong too,oops

  3. #3
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    150
    shouldnt be a problem.

  4. #4
    Join Date
    Jan 2008
    Location
    LEHIGH VALLEY, PA
    Posts
    161
    as hj says will be ok , there is no flow trough the eqauliser tube , just a balancing presure exerted on the diaphram , and have seen them and fitted them in smaller size than 1/4,

  5. #5
    Join Date
    Aug 2011
    Location
    Goose Creek ,SC
    Posts
    252
    cool I haven't noticed any difference in the way it runs , so I was figuring the size didn't matter. Thanks for the input .