Results 1 to 7 of 7
    Jul 2011
    Evolution AC Airflow Setting
    Howdy guys-
    I have an Evolution furnace (355CAV 80K BTU) with Evolution control. My AC unit is just a single stage 3-ton (non-Evolution) Bryant 116B.
    I have 4 settings on the stat for airflow control during AC operation:
    Comfort (default): This one appears to run the furnace fan at a lower speed for a while before kicking it up a notch. I assume it is to help dehumidify a little more?
    Efficiency 325: I assume this means 325CFM/ton (975CFM)
    Efficiency 350: I assume this means 350CFM/ton (1050CFM)
    Maximum: 400CFM per ton (based on the manual)
    Just curious why there are two Efficiency settings and what are the pros/cons of each? Any thoughts?
    Apr 2008
    Alberta Canada
    the lowest setting is for dehumidification, it basically overcools, where as 400 cfms will get air there quickly but leave some more humdity in air. Some people like strong fan, some people like to have more control over humidity
    I pick lower humidity
    Do it right the first time.
    Jul 2011
    Thanks for your feedback.
    Would the 350CFM/ton setting be more efficient at cooling that the 325CFM/ton setting for my 3ton unit (assuming the difference in humidity is negligible)?
    Jul 2011
    FWIW:
    Air Handler: Bryant CAC/BDP CNPVP3617ACA
    Outside Unit: Bryant 116BNA036000
    Thanks!
    Clocker
    Madison, WI/Cape Coral, FL
    What is your indoor %RH and where do live?
    Regards TB
    Jul 2011
    Quote Originally Posted by teddy bear View Post
    Regards TB
    ~43%
    SE Michigan
    Thanks!
    Jul 2002
    The way I compare it from UTC's product data @ TVA specs;
    1350 cfm = 25.72btu sensible @3.04kw 25.72/3.04=8.460
    1200 cfm = 24.22btu @2.98kw 24.22/2.98=8.127
    1050 cfm = 22.63btu @2.92kw 22.63/2.92=7.75
    looks to me like more sensible btu bang for buck at higher airflow.
    [They do not provide test data @ 325 per ton.]
    Please correct me if I'm wrong.