Thread: Stumper of the day!

  1. #1
    Join Date
    Aug 2011
    Posts
    1
    Post Likes

    Stumper of the day!

    I have a goodman crt60-1 that cools my upstairs and the same unit for my main level.

    Yesterday, I noticed the thermostat was blank, and suspected I needed to replace the battery. Upon checking, I learned the thermostat has no battery. To verify, I swtched thermostats (main level to upstairs) and found the main level thermostat was also "dead" upstairs.

    If the thermostat is blank this means there is no power being fed to it from the indoor furnace. So check I checked the breaker for the furnace, and it is ok. I even reset all the breakers. Still no power.

    I made sure that both doors for the furnace were secure. They were fine.

    I located and inspected the 3 amp fuse on the furnace control board assuming it had blown. However, it was fine.

    I know the outdoor unit has a small brown thermostat wire running into it from the inside of the home and I have disassembled the housing to make sure the wire didn't come loose or get disconnected.

    The wire was fine and I have put it all back together, yet still nothing.

    Any ideas will be greatly appreciated. I am stumped.

  2. #2
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    Time to make that call to your service company

  3. #3
    Join Date
    Jun 2005
    Location
    Winston-Salem NC
    Posts
    1,133
    Post Likes
    Quote Originally Posted by catmanacman View Post
    Time to make that call to your service company
    Ditto.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Sounds like you've taken things much farther than we'd have advised you to without special training.

    Time for a Pro to take over.



  5. #5
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    You must have a massive house!!

  6. #6
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    353
    Post Likes
    possibly a condensate float or bad condensate pump... Call a service company.
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

  7. #7
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    I see 2 options... get out a Multimeter and use the electrical schematics on the back of the furnace panel... or 2) call a pro to do the same thing.

  8. #8
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    If you took the stat off the downstairs base and stuck it on the upstairs base,and you know the upstairs stat was good right before you took it off, and the downstairs stat didn't come back to life on the upstairs base, your stat may be DOA, with nothing wrong with the unit.

    Get it checked out regardless. Something may have shorted and killed the stat. Or it's just a cheapie that died. Peace of mind will ensue if your tech elminates all causes outside of the stat itself (which in that case you may wish to invest in a higher quality thermostat...one with battery back-up).
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •