    Scope   AED     Net.Ton Rec.Ton ft²/Ton Area    S.Gain  L.Gain  Net.GainS.Loss  W.CFM   S.CFM   Sys.CFM D.Size
    Building                2.65    3.52    1,200   4,219   31,652  200     31,852  80,282  1,073   1,481   1,481
    System 1        No      2.65    3.52    1,200   4,219   31,652  200     31,852  80,282  1,073   1,481   1,481   16x16
      AED Excursion                                         66              66
    Zone 1 ( 1 Floor )              1,643   20,882  0       20,882  42,652  570     979     979
      1-Dining Room                         162     5,975   0       5,975   16,107  215     280     280     1-10
      2-Living Room                         225     2,056   0       2,056   5,062   68      96      96      1-6
      3-Kitchen                             195     1,267   0       1,267   2,600   35      59      59      1-4
      4-Study                               172     1,489   0       1,489   2,949   39      70      70      1-5
      5-Laundry Room                        123     678     0       678     2,813   38      32      32      1-4
      6-Family Room                         400     5,109   0       5,109   5,967   80      239     239     1-9
      7-Entry                               131     1,053   0       1,053   3,561   48      49      49      1-4
      8-Breakfast                           235     3,255   0       3,255   3,593   48      153     153     1-7
    Zone 2 (2nd Floor)              1,029   12,504  0       12,504  30,808  412     586     586
      9-Bedroom 1                           250     3,921   0       3,921   7,565   101     184     184     1-8
      10-Bedroom 2                          211     1,573   0       1,573   5,178   69      74      74      1-5
      11-Bedroom 3                          183     1,765   0       1,765   6,036   81      83      83      1-5
      12-Bedroom 5                          250     2,127   0       2,127   7,336   98      100     100     1-6
      13-Bedroom 4                          135     3,118   0       3,118   4,693   63      146     146     1-7
    Zone 3 (Basement)               1,547   830     200     1,030   6,822   91      39      39
      14-Family                             1,124   0       0       0       4,365   58      0       0       3-0*
      15-Exercise Room                      214     0       0       0       1,239   17      0       0       1-0*
      16-Audio/Visual Room                  209     0       0       0       1,218   16      0       0       1-0*
    How to determine ventilation requirement for basement (Zone 3, rooms 14, 16).
    Ventilation of the exercise room ( 15 )?
    Sep 2003
    I presume you want the ventilation for when the rooms are in use. What is the anticipated occupancy when the rooms are in use?
    [Edited by sadlier on 12-03-2005 at 10:17 PM]