Alarm:High Saturation Suction Temp
Guys I have a 20ton Carrier package unit.Has 4 scroll compressors 2-per circuit (R22)and its couple of yrs old.#1 runs fine and #2 after 15mins goes into this alarm.It being a RTU and 100 plus(outside of Houston,Tx),my suction is 80psi w/both compressors running and 325 high side.Feeling the liq line and compareing to the other circuit it is just alittle warm where the other is hot.For a RTU,I think that the pressures is close,but when the unit shuts off my gages indicate under charge(suction does not peg,only 80-90).Guys I know that my descriptions amounts to someone just rambling on but for now this is what I have.
If someone could explain what causes this alarm and why the unit did not trip on high super heat which (I think) is the suction line being to hot for both.I want to try and understand HSST is.The unit is 48/50AJ w/VFD and has the Comfortlink controls.Does this unit show what the SST is on the display?Thanks for any directions from a misfit----CJ
More info to come Monday afternoon
-
08-27-2011, 09:05 PM #2
Professional Member
- Join Date
- Apr 2007
- Location
- Pa
- Posts
- 738
You need to add more info. If you are saying the one liquid line temp is hot compared to the other that should point you in the right direction. Make sure coils are clean, condenser fan motors opperating and get super heat and subcooling
-
08-27-2011, 10:11 PM #3
-
08-27-2011, 10:44 PM #4
I don't know about your unit, but it sounds like it's monitoring suction pressure via~transducer and doing a conversion to temperature (hence the high SST alarm)
this alarm would lead me to believe that your controller thinks the suction pressure is above it's alarm parameters for a set time.
-
08-27-2011, 11:38 PM #5
Regular Guest
- Join Date
- Dec 2009
- Location
- Fort Worth, Texas
- Posts
- 142
unit uses thermistors. you cannot troubleshoot refrigerant problems without information. what is your superheat, what is your subcooling. are thermistors accurate. comfortlink will show you what the tempertures of the thermistors are, if the machine is using exvs it will show you % open. so first off get the manual and read it then check your thermistors and get subcooling and superheat.
-
08-28-2011, 01:26 AM #6
I suppose he'll need the manual. Should be one of these.
Comfortlink version 2.x:
http://www.docs.hvacpartners.com/idc.../48_50a-2t.pdf
Version 3.x:
http://www.docs.hvacpartners.com/idc.../48_50a-3t.pdf
Version 4.x:
http://www.docs.hvacpartners.com/idc.../48_50a-5t.pdf
Version 5.x (Current):
http://www.docs.hvacpartners.com/idc.../48_50a-9t.pdf
-
08-28-2011, 10:27 AM #7
Regular Guest
- Join Date
- Mar 2011
- Location
- Northeast Missouri
- Posts
- 61
I would agree that reading the manual to familiarize yourself with the unit should be your first step. In the alarms and alerts section it will give you possible causes to your issue. I have alot of time on this particular unit so if you can provide more accurate details (sh/sc etc) i'm sure we can help you.
-
08-28-2011, 12:46 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Well CJ I would be willing to bet you have a version 2 or version 3 software in there . There are actual pressure transducers on the suction of the compressors but thermistors on the condenser giving you that discharge pressure reading. Start your unit up earlier in the morning when it`s cooler I think your alarms are happening at start-up. Yes it show`s the SST in temps.And just confirm your suction pressure transducers for accuracy.
Last edited by Dallas Duster; 08-28-2011 at 01:12 PM.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-28-2011, 04:34 PM #9
Regular Guest
- Join Date
- Feb 2011
- Location
- colorado mountians
- Posts
- 117
Just a thought, this thing have hot gas??
-
08-28-2011, 05:59 PM #10
Regular Guest
- Join Date
- Mar 2008
- Location
- Porter,Tx
- Posts
- 30
Thanks for all the replys and it has the verison 5 controls and does not have hot gas.This is the very first problem with this unit since it was installed about 2yrs ago right before school started.I did not know about the transducers,I will check that out and see what the actural gage psi is and see what the display shows.In the book under alarm code T123 all it says is high load(which the other circuit will run)and TXV problem.Guessing what "Goodlistener" is saying that the transducer is off from actural gage pressure.Thanks for some guidence and I will go through the manual and read alittle.Hope the school dist. appreciates the outside help,I do---Carroll
-
08-28-2011, 08:03 PM #11
Professional Member
- Join Date
- Dec 2002
- Location
- Philly Area
- Posts
- 133
Hey CJ,
if it hasn't been done yet, you can increase your Hi SST alert delay from the factory setting of 10 minutes up to 30 minutes. this will allow the logic to give the unit a little more time to start bringing the RAT down before it begins to think the load is greater than the unit can handle.
-
08-28-2011, 08:22 PM #12
Regular Guest
- Join Date
- Mar 2008
- Location
- Porter,Tx
- Posts
- 30
Where can I take alook at that?Guessing Configuration,just for my own info---CJ
-
08-28-2011, 08:37 PM #13
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.


Reply With Quote