  1. #14
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    It reconfigures the L.T.B for conventional thermostats. The pain in the neck is to see if your unit is pre 93 or after 93. They change where the wires land on the LTB

  2. #15
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    Ok, ill check. It is a reliatel board. It is cool all the things u can do it just cost to much to replace.

  3. #16
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    Yeah. I like working on Trans units. They are usually pretty easy. I hate Yorks, no field experience by anyone in the factory, the electrical panel is way to small.

  4. #17
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    I'm new to commerical. So I have a lot to learn about walkins and econimizers. I don't understand yorks compressor lockouts. Is it only lock if low voltage amp draw is to high to it ? I don't understand how it sence the amps.
    Last edited by vanillaIce84; 08-31-2011 at 07:26 AM. Reason: incorrect spelling

  5. #18
    Join Date
    Oct 2007
    Location
    Richmond, VA
    Posts
    362
    Quote Originally Posted by vanillaIce84 View Post
    I'm new to commerical. So I have a lot to learn about walkins and econimizers. I don't understand yorks compressor lockouts. Is it only lock if low voltage amp draw is to high to it ? I don't understand how it sence the amps.
    With all due respect, you hijacked the thread. Why not start a new thread and talk all you want about cti boards and York compressor lockouts.

    PS. Welcome to the forum.

  6. #19
    Join Date
    Aug 2011
    Location
    fayetteville nc
    Posts
    18
    I can do that if it bothers you

  7. #20
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,326
    Quote Originally Posted by vanillaIce84 View Post
    I can do that if it bothers you
    Hello my friend and welcome to the forum!
    It's not that it bothers him, but the person who started this thread is looking for help with his Trane unit and when you hijack a thread and change the subject, it takes away from the original person looking for help. Its no big deal, we've all done it (including me).

  8. #21
    Join Date
    Aug 2011
    Location
    San Jose California
    Posts
    192
    Instead of the expense of ball valve and shell driers, recover, reinstall the relatively inexpensive factory recommended driers, and recharge?
    Our fate is ours alone to decide as long as we remain armed heavily enough to dictate it.

  9. #22
    Join Date
    Mar 2007
    Posts
    3,108
    Could be:

    Dirty coils
    Wrong fan blades
    Low load
    Overcharge
    Non-condensibles
    Undercharge
    Restricted driers

    Or any combination of any number of the above.

    I hope this is helpful. If it's not, post the following, and maybe I can offer more assistance.

    constant volume or vfd? fan speed/static press.?
    low ambient dampers?
    return temp.
    supply temp.
    mixed air temp.
    outside ambient temp.
    suction press.
    disch. press.
    liquid press.
    how many compressors running and which circuits?
    how many fans running?
    subcooling
    superheat (all 3 of them)
    press. drop across driers
    clear sight glass?
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  10. #23
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Make sure all of the condenser fans are rotating the right direction. You will bypass a lot of the coil if one of the fans is running backward. There should be a noticeable temperature drop across the drier if it's restricted.

  11. #24
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    552
    Teckster, I don't remember the part # but there is a 5 blade cond. fan that needs to be on your unit due to the low airflow here.

  12. #25

    If it helps any!

    Hello, just thought I'd put my two cents worth if it helps. If both condenser coils are clean and match the unit, make sure that the motors and blades are original and match as well. Now if other people have messed with it, I personally would start from scratch and recover, remove old driers flush system with nitrogen make sure that there are no " Restrictions ", including in the metering device. Pull a good vacuum of 700 microns or lower if possible and charge with virgin refrigerant. After all you don't know what might be in the existing refrigerant. Well hope that helps and don't give up I'm sure you'll figure it out. It sounds like a restriction of some sort. Might be within the system, or circulation of air through the condensers. Check for distinctions or irregularity in the line sizes compare circuits. Good Luck!

  13. #26
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    552
    Teckster, I don't remember the part # but there is a 5 blade cond. fan that needs to be on your unit due to the low airflow here.

    Now I know who you are just call me when you get back from vacation!!!

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event