Ok here it goes I have a Trane mod. SEHFC754N167A8AD9C01A0W00G0K000RT008000 ser. C02c01857
Let me first explain I am not a apprentice and I have a Trane unit as mentioned above that is having issues on above 95 degree days. We which is one of my top teck and I have looked at this unit and found that the condenser is under sized at the design load conditions. I will give the details we are seeing. first I live in Denver and we don't have near the air you guys do at sea leavel so here are the readings. Trying to maintain a discharge air of 55 degrees and the oat is 95 with a 30% humidity level on the day we are seeing this. Pressures are at 70 suction with a 20 degree superheat as we removed freon to confirm what we were seeing and the discharge pressure was at 410 plus and rising and it tripps at 420psi. We removed enough Freon R-22 to get as low as 4 degrees subcooling and it still tripps if all three compressors are runing. I cleaned the condenser coil for circuit #2 just to see what would happen and the unit would stablelize at 410 psi but we did notice the fan blades have been changed with 5 blade fans and they are at rated amps and this was done by trane after the oringinal install.
so here we are trying to figure this out. We disconnected one compresor on both circuits and the unit will cool the space and stay running. So I am wondering if the condenser is under sized as we removed enough freon to where the superheat will continue to rise. Any thoughts
If you find it bad 3 different ways- ~its bad~
-
08-25-2011, 11:37 PM #2
Did you pull the condensor coils apart to clean them.
-
08-26-2011, 12:16 AM #3
I know what's wrong it! The model numbers too long! Throw it in the garbage!
-
08-26-2011, 12:24 AM #4
-
08-26-2011, 12:25 AM #5
have you pulled charge an weighed?
It's hard to stop a Trane. but I have made one helluva living keeping them going.
-
08-26-2011, 01:55 AM #6
Previous techs may have left air or nitrogen in the systems. Even R410A is possible. In any event the purity of the refrigerant must be checked against a PT chart. Recover the refrigerant, test the purity, recharge with pure R22 by weight and see what happens. Restricted driers ahead of the SC temperature reading point could be hiding an overcharge.There is no reason why the discharge pressure should exceed 340 psig on a 100°F ambient. Recirculation of condenser discharge air or wind may contribute to your problem but I doubt that this would be a major factor.
"I have never let my schooling interfere with my education."
Mark Twain
More at: http://www.quotationspage.com/subjects/education/
-
08-26-2011, 08:02 AM #7
New Guest
- Join Date
- Sep 2008
- Location
- Woodsville, NH
- Posts
- 1
I agree with the above statement. must pull apart coil. with multi circiuts there is more then one coil on top of each other and from the outside coil may look clean but when pulled apart there will be a thick layer of dust. If still a problem and is believed to be first statement, then remove all refrigerant, purge, evacuate and recharge with factory amount of refrigerant. Also never hurts to call Trane tech support they are very helpfull.
-
08-26-2011, 09:06 AM #8
Hi Teckster,
The IntelliPak unit does NOT have a split coil like the Voyager II units. The IntelliPak has a single coil as Southern Mech stated.
Do the procedures that Lynn Comstock has recommended. Pay close attention to the liquid line drier, if it is stopped up and the unit was running low suction, someone may have thought the unit is low on refrigerant, and added some refrigerant. Now the unit is overcharged and running high head pressure.
The condenser is not undersized. Your unit was built in March of 2002, the temperatures have certainly been at 95 degrees or higher since then. That sort of problem would have been found before now.
Good Luck,
AllenUA Local 602
A man who says that he can't learn anything in a class is exactly right.
-
08-26-2011, 07:16 PM #9
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 869
You can also check the purity of the refrigerant by pumping down the unit, then manually run the condenser fans (no compressor), and see if the saturated refrigerant temp in the condenser matches the outside ambient temp.
-
08-26-2011, 10:07 PM #10
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
I would pull charge replace driers w/ shell driers with valves on both sides and weigh charge in. I had some units a little older than that driers were stopped up and someone had overcharged unit
-
08-30-2011, 09:16 PM #11
Regular Guest
- Join Date
- Aug 2011
- Location
- fayetteville nc
- Posts
- 18
Sorry to get off subject, i have a unit with a bad baysensorsomthing19b. Can I switch to a conventional stat by switching from the numbers to the y r g w terminals. Or is there another control ill need.
-
08-30-2011, 09:23 PM #12
Regular Guest
- Join Date
- Aug 2011
- Location
- Los Angeles, CA
- Posts
- 34
If you have the UPC board with the #'s and the letters. Yes you can switch to a conventional stat. If you have the UPC board with no connections on it, then you would need the C.T.I board. (Conventional Thermostat Interface)
-
08-30-2011, 09:28 PM #13
Regular Guest
- Join Date
- Aug 2011
- Location
- fayetteville nc
- Posts
- 18
Thanks a lot. I have seen that cti but never knew what was for.