    Ive got a 3 ton older 10 seer trane and a goodman 3 ton coil. With the .71 piston size my evap seems to be starving with only 3or 4 inches on bottom of A coil cold. I think the a coil needs a bigger size orifice. any suggestion on what size to exchange piston with to increase coil capacity. Suction line not getting as cool as needed at the service ports.
    Aug 2010
    Memphis
    what does the condenser call for
    Aug 2011
    Does the data on nameplate offer any info? manual is not avail. Whats your experience
    Aug 2010
    Memphis
    It may say but I doubt it. Go to manufactur and give model and serial.
    Aug 2010
    Memphis
    superheat, subcooling
    Aug 2011
    Gotcha, time to pull out the fieldpiece.
    Feb 2005
    GEORGIA
    Not to be a stickler about math...
    But if you have to call tech support, it is a .071..........
    Little bitty hole..
    "Value our Differences"
    Virginia
    a txv and start kit
    north suburbs of Chicago
    Hmmmm the first thing that should come to mind is that that coil did not suddenly have the wrong orifice. Has it not worked in all the years it has been installed? Plugged cap tubes?
    Aug 2010
    Memphis
    Quote Originally Posted by catmanacman View Post
    a txv and start kit
    or that
    Aug 2011
    thanks
    Thanks for the reply, I have been thinking about this. Possibly a clogged or partially clogged dryer near the compressor. My next step will be to add a txv kit. Going to check the price today.
    Tallahassee, FL
    The piston size is listed on outdoor unit data plate.
    I didnt believe I had missed that all these years....but it is there!
    10seer 3ton Trane is likely a .069-.071 though.