    I have an Intertherm electric furnace in 7 yr old manufactured home on the Oregon coast. Recently I noticed that the fan doesn't always blow at the same 'strength'. Sometimes it runs the same speed for the 30 or 40 seconds that it is on, other times it seems to run faster at the end or have a slow spot in the middle. I change the filter twice a year, we don't run it from may to september, and the wiring looks fine. Is it about to fail or is this normal and I have never noticed before?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,763
    Sounds like its time to have it serviced.

    Do you have a/c hooked to it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Feb 2002
    Location
    Toledo,OH
    Posts
    142
    Check the capacitor.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,763
    Originally posted by dugfish
    Check the capacitor.
    Last time I had one do this, it was more then a cap.

    Needs to have it looked at.

    Don't want him getting zapped by 240 volts line, or 370 to 440 off the cap.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Nov 2005
    Posts
    3
    no AC just heat

  6. #6
    Join Date
    Nov 2005
    Posts
    3

    Smile

    Thanks for your input, turned out to be the fan relay. Got it fixed and all is well. It's nice to get an idea what's going on before I call a repairman. Thanks again.