    We are in the process of installing two Trane 20 ton ac split system units and because of the layout of the property, we need to set the condenser units quite a distance away from the evaporators/air handlers. The manufacturer recommends no more than 60 feet between but it looks like the closest we can get them is 100 feet on one and 115 feet on the second.
    My question is: Can this distance be achieved without overloading the compressor? And if so, how is the best way to do so? The size of the refrigerant line is 1 1/8" copper. Is this accomplished by increasing the diameter of these lines?
    Thanking you in advance.
    Jun 2009
    Albuquerque NM
    Most manufacturers have guidelines for long linesets, and yes they may include increasing the size of the vapor line.
    The line size can be increased, but if there are any vertical segments you need to worry about velocity drop affecting oil return.
    http://www.uad.co.za/cd/pdf/technica...ion_piping.pdf
    Rochester, NY, USA
    have your TM call the factory. they will tell you what size and length you can go.
    I ran a 2 ton split---80feet total length. 20' horizontal, 22 feet vertically and another 38 feet horizontally.
    I called my local distributor, they called the factory. It's been running for a little over 6 years now with no issues
    Let the engineers do there job, if something goes wrong, it's on them
    No job to small, I can't make to big
    Jun 2009
    Albuquerque NM
    Quote Originally Posted by jmac00 View Post
    Just curious, how did you slope the horizontal segments of the line?
    Rochester, NY, USA
    Quote Originally Posted by garya505 View Post
    I didn't. I asked about slope and P-traps and they (the factory engineers)said don't bother? it will be fine.
    Jun 2009
    Albuquerque NM
    I kinda thought you might say that, but I like to ask anyway.
    Rochester, NY, USA
    good luck, give them guys a call, they're not the mean ogres everyone makes them out to be (unless you get that arrogant )