    10 DEGREE SPLIT BY DAY 20 AT NIGHT

    50 HX-036 CARRIER i recently replaced my compressor thinking it was in efficient because during the day im only getting 10 degree split. i weighed in exactly what the data plate calls for, checked my pressures and wouldnt u know it 10 degrees difference during the day 20 at night. W T H

  2. #2
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,977
    You likely have return leaks from the attic. During the day, take a temp reading near your t-stat and then go take a temp reading of the air in your return somewhere near where it enters your air handler/avap coil. Is there a big difference? Is your ductwork in the attic? You probably have the same deltaT across your evap coil, say 20 degrees, it's just that the return air temp during the day is picking up additional heat.Not to mention the additional heat gain from the attic to your supply duct air.
    Last edited by tipsrfine; 08-11-2011 at 07:42 PM. Reason: add on
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  3. #3
    Join Date
    Sep 2007
    Location
    CHANDLER AZ
    Posts
    32
    IM TAKING SUPPLY AND RETURN TEMPS AT THE UNIT ITSELF. NO EXCESSIVE HEAT IN RETURN 80 DEGREES 70 SUPPLY. SUCTION SWEATING ALL THE WAY BACK TO THE COMPRESSOR BUT NOT FREEZING

  4. #4
    Join Date
    Sep 2007
    Location
    CHANDLER AZ
    Posts
    32
    NOT SURE HOW TO GET IT ALL IN ONE AREA. I LIVE IN ARIZONA ATTIC TEMP 200 PLUS DEGREES

  5. #5
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,229
    Whats your superheat and subcooling? And what type of expansion device is being used?

  6. #6
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    799
    Quote Originally Posted by TWEEKKIN View Post
    NOT SURE HOW TO GET IT ALL IN ONE AREA. I LIVE IN ARIZONA ATTIC TEMP 200 PLUS DEGREES
    a properly ventilated attic should only be about 10 degrees warmer than the outside temp

  7. #7
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    799
    Quote Originally Posted by Tiger93rsl View Post
    Whats your superheat and subcooling? And what type of expansion device is being used?
    beer can and no bubbles....

  8. #8
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,841
    Quote Originally Posted by Gross View Post
    beer can and no bubbles....
    Well there's the problem. No science = no solutions. The days of guessing at solutions are long gone now. You need to put the science behind it and the you'll know what the problem is.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,870
    Maybe if you posted a full set of system operating conditions, we would be more able to assist you.

    With the limited information that we have, it is difficult to make any educated guesses.

  10. #10
    Join Date
    Apr 2003
    Location
    Columbus Ohio
    Posts
    96
    Quote Originally Posted by TWEEKKIN View Post
    50 HX-036 CARRIER i recently replaced my compressor thinking it was in efficient because during the day im only getting 10 degree split. i weighed in exactly what the data plate calls for, checked my pressures and wouldnt u know it 10 degrees difference during the day 20 at night. W T H
    That's good that you weighed in according to data plate but other factors
    may require more charge such as length of line set etc,

  11. #11
    Join Date
    Jun 2011
    Location
    Central Indiana
    Posts
    616
    Make sure the condenser coil is clean.
    The only true knowledge is the pursuit of knowledge

  12. #12
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,724
    Quote Originally Posted by wsykes View Post
    That's good that you weighed in according to data plate but other factors
    may require more charge such as length of line set etc,
    I think that its a packaged unit.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  13. #13
    Join Date
    Jan 2011
    Location
    Alpena AR
    Posts
    53
    Like the other post said need more info...

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event