08-20-2011, 10:26 AM #14
Old School
Hey, for 21 yrs I have heard to charge an R-22 system to 30 deg above ambient temperature on the dishcharge gauge, guess what it did work on the old systems (I use superheat or manufacturers charging chart) and after charging a system sometimes it would match up. But now you get into the high efficiency systems and there not even close sometimes, I remove refrigerant from systems all the time to get the superheat. So the moral of the story is learn the proper way now and it will save you and customers alot of compressor failures. You will be amazed how fast you will get used to it, and you will never hook up to a system without checking the superheat and subcooling. It will make you a better technician.
-
08-20-2011, 10:48 AM #15
Professional Member
- Join Date
- Mar 2011
- Location
- far southwest chicago suburbs
- Posts
- 133
I was lucky enough to have been taught about charging to superheat or subcooling in school. With dual thermometers or gauges with 2 temperature clamps I just automatically check both every time and take note. Lets you know a lot. If you have a house that is 90 degrees inside then 75 psi will probably not be close. Again you need to check everything to understand what the system is doing.
-
08-20-2011, 11:01 AM #16
Professional Member
- Join Date
- May 2011
- Location
- Houston, Texas
- Posts
- 67
Thanks, some of you guys are really compassionate and honest about this trade.
Note to self: Reread Superheat and Subcooling this weekend!
(Oh yeah! I definitely going to get that new Fieldpiece Gauge!)
-
08-20-2011, 11:01 AM #17
Professional Member
- Join Date
- Oct 2010
- Location
- SW Michigan, near Battle Creek
- Posts
- 921
yeah taking superheat and subcool as standard procedure is the way to go. and write down what the numbers are before you change annything.
The thing I see is techs not waiting long enough to get true superheat readings. the books say 10 minutes and I think that is true. subcool seems to settle down faster.
-
08-20-2011, 11:05 AM #18
Systems
of old were very forgiving. From what I saw when I first got in this trade, most systems were over-charged. As long as the system cooled, the customer didn't care. Now, everyone wants a system that will not only cool and de-humidify, but also be energy efficient while doing it. The only way to acheive this is have a properly installed and charged system following the manufacturers guidelines and using state-of-the-art test equipment. It used to be you could tune a car by changing the plugs, setting the gap with a dime, and setting the points with a matchbook cover. Try doing THAT today. Same holds true for HVAC systems. Do the job right by superheat, sub-cool, and proper airflow.
-
08-20-2011, 11:11 AM #19
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
-
08-20-2011, 11:28 AM #20
-
08-20-2011, 11:31 AM #21
Professional Member
- Join Date
- Oct 2010
- Location
- SW Michigan, near Battle Creek
- Posts
- 921
guilty secret. Fixed orifice systems work better around here if slightly overcharged.
The book is the same in New Mexico or Alaska. In Michigans low temp and high humidity I have gotten more than one call back because the system "doesnt cool as well" after I reduced the charge to the book. Add a 10-20% overcharge back in everybodys happy.
-
08-20-2011, 11:33 AM #22
Professional Member
- Join Date
- Feb 2011
- Location
- Orange County, in a Galaxy far far away...
- Posts
- 233
I think I'm the only one in my company who connects gauges, thermometers, takes indoor temps and split while unit is getting up to speed and then jots down superheat or subcool readings.
Sman3 gauges are awesome but I'm too broke to buy them. They also remove a lot of the thinking required of a technician when diagnosing and charging.You cannot cheat an honest man. But that doesn't stop people trying!
-
08-20-2011, 12:03 PM #23
Professional Member
- Join Date
- Oct 2010
- Location
- SW Michigan, near Battle Creek
- Posts
- 921
-
08-20-2011, 03:27 PM #24
-
08-20-2011, 04:55 PM #25
-
08-20-2011, 05:59 PM #26
In school we were not even taught the method the OP posted. The only time my teacher and I charge any different than the manual states is when we use Enviro Safe. Then we charge by the refrigerant manufacturers instructions. I know efficiency changes everything, in school we learned (if my memory is correct) that condenser split should be around 30 if the SEER is below 5, 20 between 5 and 9, and 10 if above 9 SEER. I may be off on the numbers a bit but I do know one rule of thumb does not work for everything all the time so I take the time to do it right. I am just starting out so I want to do everything the right way and build a reputation so I don't take short cuts unless my teacher says so (he is in charge).