Results 1 to 8 of 8
    Jan 2005
    KY
    Trane LCIR to Niagara
    Has anyone ran into issues with commissioning a LCIR device in Niagara?
    Jan 2002
    Fort Worth\Dallas, Texas
    What problem are you having?
    Go Rangers!
    NY
    I had several issues with LCIRs and zn510s. Most problems involved all or some values not showing up. In each case the problem was resolved by deleting the device in 'device manager' and rediscovering and adding again. Occassionally this took more than one attempt to come out right but now everything is working ok.
    "Controls is a lifestyle not a job" -klrogers
    Aug 2011
    ky
    ive seen it with LCIRs before, like you said, delete and rediscover always resolves that. Not sure what the deal is, however i have seen tridium panels installed with a termination module on the link, inplace of EOL resistors. I know lon says use resistors but the site i frequent the most has the termination module and if i have to re-commission a LCIr it usually takes a couple of tries. It could be the comm link causing the problem due to the lack of EOL resistors.
    Jan 2005
    KY
    The problem I am seeing is that Niagara (3.5.34) will not commission the LCIR, it always fails. I have checked the LON link and it seems to be stable with a good resistance.
    Aug 2011
    ky
    oh, the site i was referring to is running 3.4.43, might want to give niagara a call.
    San Diego, CA
    See this thread:
    http://hvac-talk.com/vbb/showthread.php?t=658001
    I ran into plenty of issues with the LCI-R. Some settings require Rover, such as PwrExhaust 'on' setpoint (based on economizer position).
    Aug 2011
    ky
    isnt that setpoint adjusted at the module on the unit