    Read the instructions first!!

  2. #15
    Join Date
    Feb 2008
    Location
    Altmar, New York, United States
    Posts
    5,175
    Quote Originally Posted by Cool_Air View Post
    Read the instructions first!!
    your doing it backwards.

  3. #16
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    444
    Quote Originally Posted by SBKold View Post
    Youre joking right?
    SEEE!

    No I was not kidding. The one that came with the coil is not necessarily the correct one.

    Customer complaint: "The company that installed this system has had to add refrigerant every spring and remove refrigerant each fall. Why is my system behaving this way?"

    Answer: Incorrect installation and setup.

    Recent: A one and a half ton condensing unit does not need 3 tons of air. The coil was mounted on a furnace with a 3 ton blower on high. Original installers replaced 3 TXV's and one compressor in the first year.

    I can't take a picture of stupidity for the wall of shame.
    Yes, I've seen that before and it doesn't mean I like it.

  4. #17
    Join Date
    May 2000
    Location
    Urbandale IA. USA
    Posts
    4,962
    Quote Originally Posted by SBKold View Post
    Youre joking right?
    NO !
    Isn't the one with the evap coil the correct one for that coil?
    I work MOSTLY with straight cooling, not HP.
    .
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.

  5. #18
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    Quote Originally Posted by cehs View Post
    NO !
    Isn't the one with the evap coil the correct one for that coil?
    .
    NO! Its a generic R22 piston.

    Usually for the largest size condensor that is a match for that coil.

    Piston size is determined by OD unit size and SEER and refrigerant type.

    Goodman has always supplied a piston chart with most replacement coils.

  6. #19
    Join Date
    May 2000
    Location
    Urbandale IA. USA
    Posts
    4,962
    Quote Originally Posted by SBKold View Post
    NO! Its a generic R22 piston.

    Usually for the largest size condensor that is a match for that coil.

    Piston size is determined by OD unit size and SEER and refrigerant type.

    Goodman has always supplied a piston chart with most replacement coils.
    Most of what I work on is straight cooling.
    I still have found that the chart shows the piston on the evap SOMETIMES, and SOMETIMES the one on the condenser.
    AGAIN there is USUALLY only 1 number difference....
    .
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.

  7. #20
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    I usually find them more than one size off myself.

    You may want to get in the habit of using the one off the condensor.

    Its the right way to do it.

  8. #21
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,361
    This thread actually turned into something.
    "I have never let my schooling interfere with my education."
    Mark Twain
    More at: http://www.quotationspage.com/subjects/education/

  9. #22
    Join Date
    Jun 2009
    Location
    Jesup GA.
    Posts
    84

    I understand now

    Thanks

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event