    Hi Velocity Needs Bigger Heat Pump?

    I have a proposal to replace window AC units with a high velocity system.

    The manual J calcs yielded 39,667 BTUh cooling load, but the proposal is for a 5 ton heat pump and 5 ton blower.

    When questioned about the difference, I was told that the lower air flow (250 cfm/ton) of a hi velocity system versus the normal 400 cfm/ton effectively "derates" the cooling capacity and the system had to be larger to compensate.

    This does not sound correct to me at all, and I thought I would ask here.


    Is there any validity to this at all?

    Thanks.

  2. #2
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    317
    I'm looking forward to see some answers on this myself. I've never heard of anyone intentionally installing with 250 cfm per ton in mind. Not enough air flow IMO. I would like to se the specs on that equipment. 5 ton is still 5 ton.
    Every problem gives us the opportunity to choose from several solutions: stupidity, ignorance, indifference, or brilliance. Which one will you choose?

  3. #3
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,120
    I think the 250 cfm/ton is measured velocity, not standardized for air pressure. I think when you factor in air pressure, it may have a high effective flow rate.

    250cfm on a conventional sytem could nearly freeze the coil in some conditions.

    Also, is the 39,667 sensible heat gain, or the total system capacity requried with latent capacity factored in. If you live in a dry climate, sensible however equals total capacity. If you're in a humid climate, a 4 tons unit for 39667 sensible might be just a tad small.

    Finally, the actual capacity of a unit at design temprature is less than the rated capacity. I don't know how much less. You might have to use the equipment data sheets from the mfg for that .

  4. #4
    Join Date
    Feb 2010
    Location
    Metro Atlanta, GA
    Posts
    394
    Strangely I had the Unico high velocity sizing guide open on my computer when I looked at this thread. What matters most in your load calculation is the sensible gain and the latent gain and the sensible/latent capacity of the equipment he's quoting. From the sizing guide:

    Equipment Selection and Size
    • Use ARI ratings to select equipment
    • Select basic unit size based on cooling load, do
    not oversize by more than 1 ton (3.5 kW)


    Unico claims a better latent heat removal because of the lower CFM per ton so if you live in a fairly humid climate this will help you out.

  5. #5
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    317
    Dang, just did my homework on the high velocity! The cfm ratings are quite different from what I am used to. Rare to see one in my area.
    Every problem gives us the opportunity to choose from several solutions: stupidity, ignorance, indifference, or brilliance. Which one will you choose?

  6. #6
    Sensible Load = 36,299

    Latent Load = 3,368

    These might help one determine the correct unit to install, but really I'm looking for comment on the idea that high velocity air handlers are "mis-rated". If you read my original post, you'll see that the the explanation for installing a much larger unit than called for by the Manual J calcs is basically: "a 3 ton hi velocity system will not really deliver 3 tons of cooling -- you need 5 tons of cooling to make up for that lower cfm."

    That sounds really bogus to me. If a hi velocity air handler is rated 3 tons, then I'm sure it has the fan/coils combination to really deliver 3 tons, under rated conditions of course.

    Any comments?

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,211
    High velocity systems don't cool a house by air exchange like a conventional system does. they cool it by aspiration. So they don't need to move as much air, they just need to move it much faster.

    Find another contractor.
    Contractor locator map

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Feb 2010
    Location
    Metro Atlanta, GA
    Posts
    394
    As weird as it seems, the answer to your question varies based on the outdoor equipment you select. Not all 3 ton units deliver 3 tons of cooling, depending on the indoor unit matchups. Upsizing by 1.5 tons from the load calc seems a little CYA to me, but depending on your contractor's experience in the area of the country you live it may be perfectly OK.

  9. #9
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,163
    Do the window units cool the home? Sort of, ok, good, great?

    How many btu are they?
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

  10. #10
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,120
    Quote Originally Posted by tedkidd View Post
    Do the window units cool the home? Sort of, ok, good, great?

    How many btu are they?

    Are the combined tons of window units a reasonable measure of cooling demand? It just seems like there's a whole lot of vairability there.

    I suspect the combined capacity of the window unit that were onc installed in my home was around 7-8 tons. Based on what I observed this last month with current split systems, I need somewhere bewteen 4-5 tons.

  11. #11
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,163
    Quote Originally Posted by motoguy128 View Post
    I suspect the combined capacity of the window unit that were onc installed in my home was around 7-8 tons.
    How many window units, somewhere between 12 & 18?

    Wow, that's a lot of window units you've got!

    Quote Originally Posted by motoguy128 View Post
    Based on what I observed this last month with current split systems, I need somewhere bewteen 4-5 tons.
    How do you arrive at that conclusion? You have twice as many window units as you think you need?
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

  12. #12
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    857

    I agree

    with BT. I would be looking for another contractor with HV experience. Maybe go to the website and find a local contractor/dealer. Wonder where is going to put all those extra vents?