    R-408A question(Evap temp) for low temp box
    For other Refer guys. Low Temp. Using R-408A, on a low temp box, what is the typical operation suction line temp/pressure?? at the evaporator? 24psi(-10) or 33psi(5 degrees)???
    Jan 2010
    Would depend on the equipment manufacturer.
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by jeremyjp View Post
    Typically a walk-in freezer evaporator is selected for a 10F TD, where the TD is the Box temperature minus the evaporator temperature.
    So for a 0F box you should expect a -10F evap temp. For R408A that would correspond to a pressure of 21 psig at the evaporator.
    Smaller, self-contained freezers tend to have slightly higher TDs like 15F or so. Then your expected evaporator pressure would be correspondingly lower.
    Jul 2009
    Northern area between Alantic and Pacific
    Quote Originally Posted by icemeister View Post
    Good info,so what TD for walk in cooler and self contained cooler? Thanks.
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by markvilleman View Post
    Don't know if I've ever heard of 408a in a med temp application. Again, it depends on the mfg. Grab a manufacturerers catalog. You can design systems with different TD's.
    Sep 2011
    Plainfield IL
    Walk in coolers and self contained coolers are usually sized at 10 degree TD.