    Thought i would let you guys know that the liquid line was blocked almost completley shut about 10 inches from condenser. Running like a champ now.

  2. #15
    Join Date
    Jul 2011
    Location
    Columbus, Ohio
    Posts
    136
    Just wondering what was the blockage.

  3. #16
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    Dont know what it was black hard as hell crap.We were thinking compressor windings so we changed out compressor had about 4 inchs of liq line plugged. I felt like a jackass for not seeing the problem. On this unit it has a sensor right before the filter dryer wrapped with insulation when i was checking it out i seen filter freezing so i changed the filter if i would have removed the insulation i would have seen it was freezing about 3 inches before filter right were it was plugged other tech found it in about 30 minutes.

  4. #17
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    524
    I had some of that stuff in a 2 ton Trane condensor once, don't know what the heck it is either. That was a couple years ago. Just replaced the condensor coil, kept the compressor. Still running after 2 years.

  5. #18
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    926
    could it be that when they did the piping that theplugs in the copper were not removed and melted when being brazed?

  6. #19
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    dont know what it was but there was a good bit of it.

  7. #20
    Join Date
    Jun 2005
    Location
    Winston-Salem NC
    Posts
    1,133
    Your problem could have been easily solved by installing something other than Trane.

  8. #21
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    yea that building has about 60 units 55 are yorks 5 tranes the last two i worked on were trane . Fixed to leaks on the one in three weeks third time replaced condenser.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event