    trane problem

    looking for a little help. Im working on a 10 ton trane hot gas reheat morginizer. When the unit starts suction pressure drops so low it opens the lps and the unit shuts off with in 5 second pressure goes back up and unit fires back up it will do this until compressor gets so hot it opens the overload. The liqiud line filter was freezeing on the evap side up to the txv so i changed both thinking i had a restriction no change. Charge is right on with the name plate i was wondering with the added coil on this unit could name plate be wrong and im under charged. suction line is warm at compressor head pressure is about 180 psi all fans are working.

  2. #2
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,579
    sure
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  3. #3
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    512
    what kind of drier did you pull out? Spun copper kind?

  4. #4
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    It was a parker filter dryer i think factory .

  5. #5
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    southern mech what does that mean?

  6. #6
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    512
    I asked because a few years ago Trane used spun copper driers that liked to puke out the desicant beads into your system, plugging every orifice. If it was a steel body drier, you have a solid core so no worries there. Never seen a morganizer, what's that some kind of proportional hot gas reheat? Dehumidification?

  7. #7
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,579
    Morganizer is a customized unit, it may need charge tweeking, give her some gas watch your S/H and S/C, discharge temp, coil temp delta T and see what it does, weigh what you put in, as you put it in.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  8. #8
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,579
    Quote Originally Posted by dunkman View Post
    I asked because a few years ago Trane used spun copper driers that liked to puke out the desicant beads into your system, plugging every orifice. If it was a steel body drier, you have a solid core so no worries there. Never seen a morganizer, what's that some kind of proportional hot gas reheat? Dehumidification?
    Morganizer is a '' customization'' company. they add ERV's, Hot water coils, Hot gas re-heat you name it. they take a Trane package unit add the element of an engineer's brainstorming and put it together, sometimes a tech's nightmare is the end result, of course isn't that what alway's happens when you put an engineer in the equasion/
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  9. #9
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    Yea its the first for me it has a another coil that sits under the unit in the supply duct that the discharge goes through before it goes to the condenser. It has louvers that open and close on the coil. I changed the dryer and txv i dont know if the beads could have got in the feeders on the other side off the txv.

  10. #10
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    512
    Quote Originally Posted by brute1 View Post
    Yea its the first for me it has a another coil that sits under the unit in the supply duct that the discharge goes through before it goes to the condenser. It has louvers that open and close on the coil. I changed the dryer and txv i dont know if the beads could have got in the feeders on the other side off the txv.
    TXV inlet should have a screen.

  11. #11
    Join Date
    Jul 2006
    Location
    pa
    Posts
    9
    thanks for your help

  12. #12
    Join Date
    Oct 2005
    Location
    Phoenix, Arizona
    Posts
    340
    Do you have any Superheat or Subcooling readings? Discharge superheat would be nice to have also. What kind of compressor does this system have?
    RTFM!!!

  13. #13
    Join Date
    Aug 2008
    Location
    S. Grand Prairie
    Posts
    244
    Quote Originally Posted by Southern Mech View Post
    Morganizer is a customized unit, it may need charge tweeking, give her some gas watch your S/H and S/C, discharge temp, coil temp delta T and see what it does, weigh what you put in, as you put it in.
    180 head pressure is low. I'd do as Southern Mech suggests and see what happens...
    Originally Posted by ladyfire3374:

    "I used to wake up excited about the challenges of the day. Now the anticipation level is somewhere between a root canal and a colonoscopy."

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event