Results 14 to 26 of 33
    Feb 2007
    Napa
    R-22 refrigerant...and the foam is not just a little foam on top, the complete sight glass is foamed...
    Nov 2009
    Richmond, working under tarps
    set SH to copeland's 8-10deg suggestion and se what happens.
    If you don't have a oil pressure or level problem I don't see the problem.
    Aug 2011
    converting from mineral to POE there should be no more than 5% mineral oil left in system
    and they are not compateable.
    These were basic rules during the refrigerant retrofits in the 90's for refrigeration
    May 2010
    Mixing of the oils is your first problem.
    Also, verify your crankcase heater is working and you are not slugging the compressor
    Nov 2009
    He is still using an HCFC, and was told by the manufact, that POE is backwards compatible.
    I believe the less than 5% other than POE applies if a HFC is being used.
    Jun 2007
    Vancouver BC
    Just wanted to agree with indy2000 regarding POE and HCFC's, this is what Copeland says about the subject:
    http://www.emersonclimate.com/en-US/...essor.aspx#Q15
    Oct 2011
    hayward ca
    How much oil was in the old compressor? If it was low, and did not leak out. it would be someware in the system , which would cause too much oil and make foam.
    Mar 2010
    central us
    mineralix oil and poe oil do not mix
    Quote Originally Posted by james32 View Post
    Beg to differ.
    I've seen POE and mineral mixed and working just fine.
    Oct 2011
    hayward ca
    So whats the verdict here man....... Elvis..........We need an Elvis sighting here...
    Oct 2011
    hayward ca
    So whats the verdict here man..??..... We need an Elvis sighting here...I'm very curious what the outcome here will be. I'm taking notes here.
    Nov 2011
    British Columbia
    Old thread, but couldn't help it, made me curious. With elvis66 MIA, I think indy2000 has called it on this one. No need to worry if level present and not tripping.
    One thought tho... POE has more detergent qualities and is more miscible than mineral oil. It will disolve in and out of refrigerant faster than MO especially in HCFCs. That being the case, "foaming" at the crankcase is not unrealistic.
    Feb 2007
    Napa
    The outcome was that oil pressures was pretty stable at about 40 psi, and since there doesn't seem to be a definative answer, I am just going to accept it's foamy oil personality and call it good.
    Thanks for all the input, you all really got me going in the right direction.