    Hello guys
    This is my question
    TXV system. Refrigerant is boiling off at 25f. TXV maintaining 12f of superheat at the end of the evaporator. Since most of the evaporator is below freezing, won't it freez up?
    I was told by one of our top techs that if ( she's a sweating a TXV is ok with those temps ) Is that true?
    Doc I hope you read this
    Thank you guys
    Oct 2005
    Need to know the dewpoint of the entering air, it won't freeze if there is no water.
    Apr 2002
    Dallas, TX
    As titleless notes, entering air dewpoint would need to be known. And air velocity across the coil would prevent ice from forming on the evaporator surface if dewpoint were 25°F or slightly higher.
    Off-cycle defrost is the norm for medium temp applications like this if icing becomes a problem.
    use the charging
    charts that come with the equipment, you can never go wrong. Anything else is a guess
    Is this for a/c, or a cooler.
    A TXV does not control coil pressure nor does it control coil temperature. It controls superheat. No matter if you have a TXV or a piston, you will frost the coil at 25 degrees. (barring a superhigh sensible only load).
    A 25 degree coil would be suitable for a cooler and will require compressor off cycle defrost on occasion.
    Now if this were comfort cooling the problem indicates a low load which is either low airflow or a cold return. Dont look for a TXV or any other metering device to overcome a low load. You can thank your TXV, however, for protecting your compressor from being flooded.