Thread: Trane model E
    Jun 2010
    northwest connecticut
    Trane model E
    I have a trane model e 8 cylinder ! year old [replacement] lost oil pressure . 15 psi on start up then drops off to almost nothing. going to do a visual inspection this week. Does anyone have a pdf for HCOM-SB-39a this would be greatly appreciated . Thanks!!!
    The Hot South
    Here you go.
    Attached Files Attached Files
    Jan 2005
    Houston TX
    Model "E" for enough
    hvac 1966 - I think you find a leaking "O" ring on one of the cylinder actuators. There could be as many as 5 loading cylinders in that puppy and it requires oil pressure to load up. Compressor will start unloaded (either hydraulic or electrical ) makes no difference. I could be wrong by I think net oil should be 50 - 55#'s. Have fun It's been quite a while since I tore one down. _Geo
    Of all the things I have lost in my life, I miss my mind the most-GEO
    Jun 2010
    Thanks you i appreciate the help!!!!!!!
    Mesquite Tx.
    There is a relief valve located on the pump end bearing housing. If this valve gets stuck open, you will have an immediate drop in oil pressure. If you pull out the bearing housing, it will be the valve held in place by a cotter pin. I have pulled out the pistons and liners that stay loaded, and the handhole cover opposite the unloader control, and hook an electric oil pump up to the oil pressure port, and look inside to see where all the oil is going. Good luck.
    Nos operor non pensio volutabrum