    coleman coil

    help?? Just installed new coleman 2 ton 410a a/c with horizontal coil with txv with a 60,000 btu 80 % heater in attic. Only half of coil getting cold. Can not get subcooling or a good split. I changed txv 2 times. Also replaced freon 3 times. no change???

  2. #2
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Confused

    Quote Originally Posted by lioni hvac View Post
    help?? Just installed new coleman 2 ton 410a a/c with horizontal coil with txv with a 60,000 btu 80 % heater in attic. Only half of coil getting cold. Can not get subcooling or a good split. I changed txv 2 times. Also replaced freon 3 times. no change???
    curious, coming off the furnace, do you have a nice transition duct the longer the transition duct the better,so it spreads out the airflow so it catches the whole coil?

  3. #3
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    coil is on furnace

  4. #4
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    I did the same system last week it works fine.

  5. #5
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Confused

    Quote Originally Posted by lioni hvac View Post
    coil is on furnace
    yeah i got that, but the coil is horizontal, correct? which means its lying on its side, did the other coil have a a-coil or a horizontal coil. what was wrong with the old coil? was this a easy swap, or did you modify the duct coming off furnace! how much space is from the furnace top to the horizontal coil.1 ft. or is the coil jammed up against the furnace and did you just fill in the gaps with tape/metal, trying too get a mental picture here!

  6. #6
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Confused

    Quote Originally Posted by lioni hvac View Post
    I did the same system last week it works fine.
    ok maybe one of the pros has a suggestion, good luck!

  7. #7
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    case coil system laying on its side a coil

  8. #8
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Hmm

    Quote Originally Posted by lioni hvac View Post
    case coil system laying on its side a coil
    how long have you been doing this type of work, do you have a co. or work for some one?

  9. #9
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    company 15 years first time this happen to me and my friends

  10. #10
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    Reuse lineset? Purge lineset? Evacuation to what micron level? Feed tubes freezing one side only? What is the superheat and subcool values? Airflow measured?

    More information and maybe a few pics may help.

  11. #11
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10

  12. #12
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    Also feed tubes does not freeze with system not running.

  13. #13
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    1,058
    Post Likes

    Are these

    Quote Originally Posted by lioni hvac View Post
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
    readings correct? You only have 3 degree subcool?

  14. #14
    Join Date
    Mar 2007
    Location
    South Texas
    Posts
    239
    Post Likes
    had one one time installers installed txv didn't take out the flow rater, low suction poor split unit was charged by subcooling to specs

  15. #15
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    Yes i removed flow rater.

  16. #16
    Join Date
    Apr 2003
    Location
    Columbus Ohio
    Posts
    96
    Post Likes
    sounds like you got a bad evap coil form the factory and its restricted
    get your post up and get your pro membership and post this on the pro side

  17. #17
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    You need to know subcool and superheat. Your subcool should be higher than 3. Sounds undercharged. What was the superheat?

  18. #18
    Join Date
    Aug 2008
    Location
    S. Grand Prairie
    Posts
    244
    Post Likes
    Quote Originally Posted by wsykes View Post
    sounds like you got a bad evap coil form the factory and its restricted
    get your post up and get your pro membership and post this on the pro side
    Ditto
    Originally Posted by ladyfire3374:

    "I used to wake up excited about the challenges of the day. Now the anticipation level is somewhere between a root canal and a colonoscopy."

  19. #19
    Join Date
    Aug 2012
    Location
    Tennessee
    Posts
    67
    Post Likes
    Orifice clogged from install?

  20. #20
    Join Date
    May 2006
    Location
    Vancouver, U.S.A.
    Posts
    482
    Post Likes
    Any filter dryers that could be pluged?
    Air conditioning to all and to all a good night

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •