had one one time installers installed txv didn't take out the flow rater, low suction poor split unit was charged by subcooling to specs
-
Yes i removed flow rater.
-
sounds like you got a bad evap coil form the factory and its restricted
get your post up and get your pro membership and post this on the pro side
-
You need to know subcool and superheat. Your subcool should be higher than 3. Sounds undercharged. What was the superheat?
-
 Originally Posted by wsykes
sounds like you got a bad evap coil form the factory and its restricted
get your post up and get your pro membership and post this on the pro side
Ditto
Originally Posted by ladyfire3374:
"I used to wake up excited about the challenges of the day. Now the anticipation level is somewhere between a root canal and a colonoscopy."
-
Orifice clogged from install?
-
Any filter dryers that could be pluged?
Air conditioning to all and to all a good night
-
 Originally Posted by Cmstech
Orifice clogged from install?
Negative points for


jim
Common sense isn't very common anymore.
-
only half of coil getting cold? 3 degree SC? not sure what spilt is... If its milk, you aint supposed to cry. I know that. I've heard old timers call the temp difference the "split". If thats what you're talking bout, 10 just wont do. I'm probably wrong but I'm thinking under charged.
-
get your subcooling up to 10 and see what happens.
It sounds like you're undercharged.
-
 Originally Posted by lioni hvac
Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
Are you saying you ran the ac with no blower? This would sure cause all your tubes to freeze.
You need to put the phone down and get back to work!