had one one time installers installed txv didn't take out the flow rater, low suction poor split unit was charged by subcooling to specs
-
08-14-2011, 09:45 AM #15
Regular Guest
- Join Date
- Aug 2011
- Posts
- 8
Yes i removed flow rater.
-
08-14-2011, 10:30 AM #16
sounds like you got a bad evap coil form the factory and its restricted
get your post up and get your pro membership and post this on the pro side
-
08-14-2011, 08:39 PM #17
Professional Member
- Join Date
- May 2009
- Posts
- 247
You need to know subcool and superheat. Your subcool should be higher than 3. Sounds undercharged. What was the superheat?
-
08-14-2011, 11:04 PM #18
Professional Member*
- Join Date
- Aug 2008
- Location
- S. Grand Prairie
- Posts
- 243
-
08-06-2012, 10:58 PM #19
Professional Member
- Join Date
- Aug 2012
- Location
- Tennessee
- Posts
- 62
Orifice clogged from install?
-
08-07-2012, 01:02 AM #20
Any filter dryers that could be pluged?
Air conditioning to all and to all a good night
-
08-07-2012, 02:19 AM #21
Professional Member*
- Join Date
- Sep 2010
- Location
- Western, MO
- Posts
- 777
-
09-10-2012, 02:28 AM #22
Regular Guest
- Join Date
- Sep 2012
- Location
- mid georgia
- Posts
- 6
only half of coil getting cold? 3 degree SC? not sure what spilt is... If its milk, you aint supposed to cry. I know that. I've heard old timers call the temp difference the "split". If thats what you're talking bout, 10 just wont do. I'm probably wrong but I'm thinking under charged.
-
09-10-2012, 08:16 AM #23
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,640
get your subcooling up to 10 and see what happens.
It sounds like you're undercharged.
-