09-10-2012, 10:15 AM #1
Rheem Condenser with fluxuating pressures and temps.
Just replaced an evap coil on an R-22 system. Had bad leak in an Aspen coil on a 5-6 year old system. It has an orifice on the coil. The day I installed it it was working well. Had a call out about a month later, upstairs not keeping up. Its a 2400sqft two story with 1-5 ton system. Suctions pressure was going up and down from about 60-75 ranging from 7-18 degree superheat. Couldn't read high side due to leaking high side hose on previous call. Checked indoor coil drop and was getting a fluxuating split of 14-18 degrees. Had a lot of temp loss in ducts from super hot attic. About 7 degrees. I plan to go back out there to get a couple more reading but was curious if anyone had some ideas what could be doing this.
Thanks.
Jr
-
09-10-2012, 12:59 PM #2
When you changed the coil, did you recover old refrigerant or pump down & keep it? We found we were getting moisture in the systems when they were leaky and stopped trying to save the remaining gas. Starting all new stopped the expensive callbacks.
-
09-10-2012, 01:08 PM #3
Professional Member*
- Join Date
- Sep 2003
- Posts
- 1,432
Non-Condsensibles?
-
09-10-2012, 01:22 PM #4
We pumped the system down and topped it off after vacuum. We were pretty careful with the system before we changed the coil so I figured the refrigerant was ok. I guess not careful enough.
-
09-10-2012, 04:09 PM #5
Professional Member*
- Join Date
- Dec 2003
- Location
- Citrus County, Florida
- Posts
- 1,231
When I have a leaker, I recover most of the gas and then use another recovery tank for the rest.This eliminates sucking in the atmosphere.
Doug
-
09-10-2012, 05:31 PM #6
We would pump down the charge in the past but got stung too many times with situation like this. So from about 2 years ago on, recover all then all new gas .
-
09-10-2012, 07:20 PM #7
hope you figure it out. but next time cant you use the low side or charging side hose and just screw it to the hi side?
-
09-10-2012, 09:44 PM #8
Regular Guest
- Join Date
- Jul 2011
- Posts
- 79
non-condensables..
bucking compound gauge.. need to recover the refrigerant and put new in... after you pump it down... Might wanna add a filter dryer as well.
Sorry bro...


Reply With Quote