Results 1 to 13 of 24
Thread: coleman coil
    Aug 2011
    coleman coil
    help?? Just installed new coleman 2 ton 410a a/c with horizontal coil with txv with a 60,000 btu 80 % heater in attic. Only half of coil getting cold. Can not get subcooling or a good split. I changed txv 2 times. Also replaced freon 3 times. no change???
    Aug 2011
    Confused
    Quote Originally Posted by lioni hvac View Post
    curious, coming off the furnace, do you have a nice transition duct the longer the transition duct the better,so it spreads out the airflow so it catches the whole coil?
    Aug 2011
    coil is on furnace
    Aug 2011
    I did the same system last week it works fine.
    Aug 2011
    Confused
    coil is on furnace
    yeah i got that, but the coil is horizontal, correct? which means its lying on its side, did the other coil have a a-coil or a horizontal coil. what was wrong with the old coil? was this a easy swap, or did you modify the duct coming off furnace! how much space is from the furnace top to the horizontal coil.1 ft. or is the coil jammed up against the furnace and did you just fill in the gaps with tape/metal, trying too get a mental picture here!
    Aug 2011
    Confused
    ok maybe one of the pros has a suggestion, good luck!
    Aug 2011
    case coil system laying on its side a coil
    Aug 2011
    Hmm
    how long have you been doing this type of work, do you have a co. or work for some one?
    Aug 2011
    company 15 years first time this happen to me and my friends
    Mar 2009
    Triad - North Carolina
    Reuse lineset? Purge lineset? Evacuation to what micron level? Feed tubes freezing one side only? What is the superheat and subcool values? Airflow measured?
    More information and maybe a few pics may help.
    Yes, I've seen that before and it doesn't mean I like it.
    Aug 2011
    Yes reuse lineset, yes purge linset, Evacuation good. I pulled blower motor wire and ran a/c All feed tubes froze. Subcooling 3, airflow good my spilt is 10
    Aug 2011
    Also feed tubes does not freeze with system not running.
    Frederick, MD
    Are these
    readings correct? You only have 3 degree subcool?