    I have two zones on my Burnham forced hot water boiler. It turns out that the zone 2 thermostat is poorly placed and the zone 1 thermostat could be adequate for the whole house. Is there an easy way to run both zones from the same thermostat? Is that what Zone 1 priority means?

    Hope this isn't too DIY and thanks for your help.

    Ed

  2. #2
    Join Date
    Feb 2003
    Posts
    1,996
    You could just wire the 2nd zone circulator or zone value to the other zones so it would turn on/off at the same time.

    Beter yet, I'd just relocate the other thermostat. Nice to be able to lower bedrooms during the day, liviing room/kitchen during the night when each gets little use. (If the piping is zoned that way of course)

  3. #3
    Join Date
    Feb 2005
    Location
    Toms River, NJ
    Posts
    425
    Yes there is a very simple way but unfortunately It am not allowed to tell you. I would violate the rules I believe...Sorry

    P.S. To answer your second question....no that is not what Priority means. Zone 1 Priority means that you when zone 1 calls for heat (usualley domestic hot water) you do not allow the other zones to come on until zone 1 is satisfied.