    Aug 2011
    Kansas City, MO
    Lennox 10HBP42 question
    Hi - recently had my heat pump serviced. Just chatting with the technician I mentioned that my house is always warm in the summer (we keep it at 78 and the master on the first level gets up to about 82-83) and cool in the winter. This unit is servicing approx 4500 sq ft (ranch style with finished walk out) - he stated that on some older Lennox models the calculations were off by Lennox. Is this a correct statement? He got back with me and the ARI ratings show this unit to be 3.17 ton with my coil (C26-41) and not 3.5 ton.
    Thank you!
    Virginia
    That is the same with all manufactures ,this s the reason that a load calculation needs to be performed and the unit selection needs to match the load, sounds like you need a bigger unit and some duct modifications
    burlington county n.j.
    hook a 3 1/2 ton unit up to a 3 ton coil you can't expect to get 3 1/2 tons worth of cooling out of it.
    depending on coil match that unit could be closer to 4 ton cooling capacity.