Results 1 to 13 of 15
    Aug 2011
    maryland
    power factor capacitor
    I had a power factor capacitor blow up on a 460v starter for a trane cvhe. i disconnected both capacitors and the motor seems to be running just fine. is there any issue with just leaving them disconnected and not replacing them? they are strictly accessories , right ?
    Aug 2009
    Ontario, Canada
    You can get them way cheaper at an electrical supplier than through Trane. Just go to your local ABB dealer and take the Cat#.
    You can run without them but they may pay more to run it.
    Aug 2011
    maryland
    thanks will do
    The Hot South
    You can run the chiller without them but the chiller will use more power. They're accessories.
    Jan 2005
    Houston TX
    Power factor correction capacitors
    post time- The motor operating the centrifugal compressor has a power factor of about .70-.85, that is the volts-amps that are actually being used as compared to the design volt- amps. The actual figure incurs losses due to inductive reactance. The PFCC's put a leading capacitive reactance to counteract these losses and bring your motor power factor up to .95-.99. Unity or a power factor of 1.0 would be detrimental to the motor so we never attempt for a unity reading. Your electrical provider puts penalties on commercial facilities with lower power factor as this a waste of energy that isn't being of beneficial use that they still have to provide to run your equipment. I totally agree with R123, get your applied voltage rating and somewhere on the original PFCC's there should be a KVAR number depending on your actual motor horsepower. Give them these numbers and you should be good to go. Good luck and be safe out there.-Geo: angel:
    Having sex is like playing cards, if you don't have a good partner, you better have a good hand. !!!!!!
    The Hot South
    That's a great explanation George.
    Jan 2005
    Houston TX
    Thank you
    R-123- Now you've gone and done it, you're making me blush !-Geo
    unity power factor correction is actually ok...it is the OVER correction that can be bad.
    if you do decide to replace the capacitors, make sure that you are wiring them up properly. the capacitors should be on the motor side of the contactors...not the power side of the contactors. if you are not sure, contact a qualified chiller technician or electrician.
    i saw a manufacturing plant that had capacitor banks everywhere. they also had a PFCC on the wrong side of the contactors of the chiller. as soon as the chiller shut down, the capacitors were 'correcting' everything else in the building. every once in a while, 'pop' goes a capacitor...sometimes 'BOOM' goes a capacitor.
    Jan 2005
    Houston TX
    Jayguy ever hear about....
    Jayguy- I try to limit any power corrections to .97-.99 where economically feasible by customers purse strings. When I took class's on this topic we were taught to never go to unity (1.0) or above because of over excitation and over speed. While we are discussing this I have a question for you. Wye-Delta, closed transition starter, PFCC wired to the load side of the 2M (run) contactor. I would think Load side of 1M (starting) contactor would put them online sooner. I have seen them all over a central plant including switch gear way ahead of the starter for each individual chiller. The ironic part was these were either electronic soft starters of VSD Yorks. I tried to explain to the customer that he didn't need PFCC on these units and showed him in the York literature where the factory had said thats a no, no. If you can get a good motor reaction from unity without damage to equipment more power to you, literally.
    -Geo
    Jul 2001
    maryland
    this thread is a good read, one of the best I've read here.
    Saving the world...one service call at a time.
    Quote Originally Posted by ga1279 View Post
    -Geo
    i guess my point was that unity is OK by definition. if i found a unit running at or near unity, i would not be worried (because i am not liable for it), however, i would not engineer to unity without a very good power quality study...even then, i would still not correct to unity. typically, correcting to 90-95% is what i find stated in most manufacturers manuals.
    as for the wye-delta, i would wire it to the 2M only because during the start up, you may be over-correcting (even if it is only for the few moments before transition).
    PFCC's between the utility and the starter are acceptable (although they are probably not needed) but between the VFD/soft starter and the motor is a very big no-no, however, some people do confuse 'filters' (which have capacitors in them) with PFCC's. this business is getting confusing and fun at the same time. i have learned a ton since i bought my Fluke 435!
    Jan 2005
    Houston TX
    PFCC's
    jayguy- That's about the way I size it up, Thanks for thw answer to the 2M question. I had a rather vivid discussion with an electrician concerning this point, he stated that being on the load side of 2M it was always in the circuit. I drew out the circuit in an attempt to explain that it wasn't, well you know the rest- Geo
    i love electricians!
    "whadda you mean 'phase rotation tool'? oh. i think that Jim has one. other than that, i have only heard of them."
    1 phase rotation meter in an electrical contractor company is like 1 manifold set in a HVACR company.