    Bad Duct Installation in New Home

    Hi Everyone,

    I am in need of advice. I live in CA, and I bought a new model home a few years ago. I had issues with my HVAC split system a few weeks ago. My home is two levels at a total of 2500 sq ft. My AC Heating is a 5 ton unit, which you all know produces 2000 cfm, but I only have one 20 x 30 return of 1200 cfm on the second floor. There is no return on the first floor and it gets very humid at night. It's going to be impossible to have a return on the first floor now.

    Do I have any grounds of making my home builder install a second return? Is there a construction standard on how duct work is installed? What facts can I use to back up my claim?

    Thanks for your assistance.

    The King

  2. #2
    Join Date
    Jan 2011
    Posts
    92
    Post Likes
    A return on each level is code in NC. Don't know about CA though. A single 20x30 return grill on a 5 ton is disgraceful. Its doing more than killing your efficiency, it's killing your unit.

  3. #3
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    I doubt its the lack of a 2nd return causing your high humidity generally speaking low airflow causes ac units to be great dehumidifiers ,I suspect the problem is 5 tons of ac for 2500 square ft on a newly constucted home I would demand the load calculation that they used to backup the reason for such a large air conditioner

  4. #4
    Join Date
    Aug 2011
    Posts
    3
    Post Likes
    Thread Starter
    I really am going to need more help on this one. My home builder told me that they aren't obligated to put in the 2nd return, and the numbers of CFM are just "speculation." I did ask for the load calculation for my home, and I was told that it's proprietary information.

    Any thoughts on how I should approach this now?

  5. #5
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    Quote Originally Posted by KingQA View Post
    I really am going to need more help on this one. My home builder told me that they aren't obligated to put in the 2nd return, and the numbers of CFM are just "speculation." I did ask for the load calculation for my home, and I was told that it's proprietary information.

    Any thoughts on how I should approach this now?
    In other words they don't have one because they guessed at the size , I don't see how it would be proprietary it's not like it can use it for other houses . Or on the other hand maybe they have a one size fits all load calc and there fore that's the problem. I thought in the great state of Cali they had to summit a load calc with the application for a permit . Any how they are shams

  6. #6
    Join Date
    Feb 2010
    Location
    On the water but near the hood
    Posts
    1,813
    Post Likes
    You will rarely if ever see a return for each floor on a tract home in California. That argument is a dead end. Architects won't allocate any room for the duct work and soffit to conceal, and buyers would rather blow their mechanical budget on non-comfort items such as granite and tile.

    What's the story with your neighbors systems? Are they sized similar to yours? What happens with continuous fan operation?

    Let the great return location debate begin.

    Any thoughts on how I should approach this now?
    Go see what the builder submitted to the city Building Dept for your house, they may still have records

  7. #7
    Join Date
    Aug 2011
    Posts
    568
    Post Likes
    how about getting a whole house dehumindifier?????

  8. #8
    Join Date
    Aug 2011
    Posts
    3
    Post Likes
    Thread Starter
    I think I'm SOL. Apparently there is a 4 year statute of limitation to file a claim against a contractor in California. My home is a model home so it was built more than 4 years ago. It's a shame that some contractors are allowed to get away with horrible workmanship.

  9. #9
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by KingQA View Post
    I think I'm SOL. Apparently there is a 4 year statute of limitation to file a claim against a contractor in California. My home is a model home so it was built more than 4 years ago. It's a shame that some contractors are allowed to get away with horrible workmanship.
    You may want to check on that with the registrar of contractors. If you are the first to live in the home that rule may not hold true!
    California has whats called title 24 and a load calc has been required for years, the statue of limitations I believe is seven years for construction defects as far as filing suit.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  10. #10
    Join Date
    Oct 2004
    Location
    Palm Desert home, Bear Valley Springs home & Maui condo
    Posts
    4,126
    Post Likes
    Model homes typically have oversize units to compensate for doors opening & closing all day long, no window coverings or shade & large people loads. I wouldn't be surprised if the non model in your floor plan uses a 4 ton.

  11. #11
    Join Date
    Apr 2005
    Posts
    53
    Post Likes
    When was the Notice of Completion filed? Sometimes builders hold off filing those until the hold is sold. The 4 years would start from that date.

  12. #12
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,846
    Post Likes
    Sometimes it's just more cost effective to play the hand you're dealt. In this case a long legal battle still won't improve your comfort and it'll likely cost you more to litigate than it would to fix it. So here are my limited suggestions:

    A. Have a qualified and competent company give you a proposal to replace the existing system with a properly sized system, naturally using Manual 'A'. Also have them check the duct system to see if any modifications need to be done.

    or

    B. Have a qualified and competent company give you a proposal for a whole house dehumidifier that will operate independently of the cooling system. This would relieve your high humidity issue at lower cost than replacing the AC system and when it does come time to replace the AC for other reasons, then you can address sizing at that time. And you can keep the WHD too.

  13. #13
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes
    I agree with catmanacman and Precision has a really interesting thought on the reason why your unit may be oversized. But to answer your question directly
    1.Unit size does have more to do with excessive size and not duct
    2. return grill is 600 sq Inches, 300FPM face velocity, so siized right but does air have a path ie transfer duct from a room if door closed?
    3. Check, 4 years may be from date when problem discovered. If the builder didn't pull the loads and the code required it then he is never covered by statute of limitations because he never did it right in the first place.
    4. Doesn't your state energy law or utility co require a load calc. It is your house you need to see it. Again find out if original permit building drawing required this info.

    Check my profile for email and other contact info if you would like to discuss this offline.

    Mike
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  14. #14
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    5 ton on a 2500sqft new construction home in CA? Yikes. With good windows and insullation, I'm thinking most like 3-4 ton, but you'll need a heat load calculation.

    Ideally, if feasible, the best set-up woudl be a 4 or possibly even a 3 ton 2 stage unit and split the upstairs and downstairs into 2 zones.

  15. #15
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    The lowest cost solution might be to just replace the outside condensor unit only with a smaller unit based on a proper load calculation. Having a 5 ton coil on a 4 ton unit is acceptable.

    No need to repalce the entire system IMO.

  16. #16
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    The lowest cost solution might be to just replace the outside condensor unit only with a smaller unit based on a proper load calculation. Having a 5 ton coil on a 4 ton unit is acceptable.
    I doubt that would solve the humidity issues. Most parts of California cool off pretty well at night, so the heat gain to the house can fall off substantially a few hours after sunset. Compared to where I live, when we were hitting 105-108 degrees for daily highs, it often would not drop below 100 until around 9 PM.

    OP stated it was a two story house. If the thermostat is on the first level (and I'm assuming there's only one system on this house) this problem alone is aggravated by two factors: summer reverse stack effect AND oversized equipment. The downstairs stays cool more readily due to thermal gradient characteristics of a two story house, meaning the system runs less, thinking there's not much load. The less the system runs, the less it can dehumidify. If the OP pushes the stat colder to get dehumidification, the first floor overcools and then feels clammy.

    A whole house dehumidifier might be an option in this case, but it would still leave the OP with an oversized HVAC system. That said, the dehumidifier may allow the occupants to live in higher room temperatures before cooling would be needed. It's just a shame he's in a corner like this.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  17. #17
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Lets start over instead of offering solutions before we find the problem.
    What is the inside temp/%RH?
    What is the outside dew point overnite?
    How many occupants?
    Overnite setting of the t-stat?
    On/Off minutes ofcycle time of the A/c?
    How much water is the a/c removing during day and at night?
    Keep all of the inside doors open as much as possible to provide indoor circulation with pressurization/depressurization.
    Extreme coastal climates in CA can have high enough dew points to require supplemental dehumidification. Also occasional wet cool weather may cause indoor humidity problems. When the outdoor dew points are <55^F, adequate fresh air ventilation will maintain reasonable indoor %RH. Keep in mind that occupants add a considerable amount of moisture to an unventilated space. All homes need an air change in 4-5 hours to purge indoor pollutants and renew oxygen. When the outdoor dew point is <50^F, fresh air reduces indoor %RH. When the outdoor dew point is +55^F, adequate fresh air ventilation plus the moisture from the occupants needs several lbs. per hour dehumidification. If the a/c is operating enough, no problem. When the a/c is not operating enough, supplemental dehumidification is needed to <50%RH.
    Give us the information requested and we will be able to give some intelligent solutions.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  18. #18
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Confused

    Quote Originally Posted by teddy bear View Post
    Lets start over instead of offering solutions before we find the problem.
    What is the inside temp/%RH?
    What is the outside dew point overnite?
    How many occupants?
    Overnite setting of the t-stat?
    On/Off minutes ofcycle time of the A/c?
    How much water is the a/c removing during day and at night?
    Keep all of the inside doors open as much as possible to provide indoor circulation with pressurization/depressurization.
    Extreme coastal climates in CA can have high enough dew points to require supplemental dehumidification. Also occasional wet cool weather may cause indoor humidity problems. When the outdoor dew points are <55^F, adequate fresh air ventilation will maintain reasonable indoor %RH. Keep in mind that occupants add a considerable amount of moisture to an unventilated space. All homes need an air change in 4-5 hours to purge indoor pollutants and renew oxygen. When the outdoor dew point is <50^F, fresh air reduces indoor %RH. When the outdoor dew point is +55^F, adequate fresh air ventilation plus the moisture from the occupants needs several lbs. per hour dehumidification. If the a/c is operating enough, no problem. When the a/c is not operating enough, supplemental dehumidification is needed to <50%RH.
    Give us the information requested and we will be able to give some intelligent solutions.
    Regards TB
    hey,nice post, that's why you make the big bucks$ goOOO,RIPON,WIS!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •