Just started up 3 ton Rheem on open cell foam new construction. Foam on outside walls and roof rafters. Was 96 in house yesterday when I started unit, ran all night, checked at 7 am this morning, only pulled down to 83 inside.
This is giving me a bad feeling in my stomach if you know what I mean.
House is 2600 sq. ft. It also has been extremely hot here. 106 and 107 day after day. The design temp for this area is 97.
Question , how should I handle the ceiling load calc when the insulation is up on the roof rafters. Now the whole attic space is being cooled .
I may be ripping this system out and going larger.
You could install return ducts into the living space ceiling, add insulation so you dont have the attic load to the house.
Do you have a heatload calculation?
I used wrightsoft. But maybe my data entered was off for the ceiling load.
I was thinking about insulation above the ceiling to remove or lessen the ceiling load.
Just talked with another local contractor a they are sizing the units the same regardless of the type of insulation used. That being said this would have been a 4 ton unit.
Air2spare when u say add returns in ceiling, you would also tie them into the return plenum at unit. Right.
Done a few foam houses, I always size the same as non foam as well.
You have a few things to check before going off the deep end. The refrigerant change and air flow over the cooling coil are the starters. Over charge or undercharge will reduce btus moved. The coil temp should be 25^F below the return air temp. Lower coil temp improves latent removal and but slows sensible cooling. In your case, to improve the sensible cooling, you could start with -20^F coil temp.
What is the situation on fresh air ventilation? Limit the fresh air to 70 cfm when occupied.
Also, are all of the blinds and window covers inplace? Solar gain is a killer that can be slowed with shade, blinds, or other ways.
More info on the temp/%RH, coil temp, and superheat/subcool. Is the outside condenser clear of obstructions and free air flow.
Regards TB
Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
Around here, a 2600 sq ft house would usually have a 3 ton even with R11 walls and some blown in the attic. We just came off a stretch of upper 90s and very high humidity and people did just fine.
I'm with the rest, give the place a chance to cool down & dry off and see how it does.
I remember my foaming buddy telling me of a job where the HVAC sub oversized the equipment since he didn't believe the size the calc called for. HO had lots of humidity issues.
Another thought. Make sure you do not have a kink in the suction line going back to the compressor. Also extra long suction line without upsizing. Both really kill capacity.
Good luck
Regards TB
Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
When we first started doing foam houses we didn't trust the load calc but stuck with it and have not had the first problem. Approx 3200sqft with a cool 2.5 tons. At start up I was kinda feeling like we may have some issues. Told HO we would be back in two days, when I returned she had the biggest smile ! Give it some time. No one has mentioned AIR FLOW so that may be something to check? This is also in south LA . ALL FOAM HOMES GET HEAT PUMPS unless HO refuses.
Hey Timber, is the air handler & ductwork in the attic? My understanding about foamed attics at the roof is that there is an increase to the cooling load compared to traditionally insulated attics at the ceiling, but if the ductwork is in the attic, then there is a net reduction to the cooling load due to having brought the ductwork into the conditioned area.
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com
106 and 107, day after day?
I'd give it another day before I decided anything was wrong. You have to pull out all the humidity and cool down the structure before it will run "normally".
Let us know how it's doing tomorrow.
Use heat rise method to determine enough cfm delivery.
measure delta across the coil and measure coil capacity.
measure static pressure