Page 1 of 4 1234 LastLast
Results 1 to 13 of 50

Thread: TXV hot swap

  1. #1
    Join Date
    Mar 2010
    Location
    Fayetteville, AR
    Posts
    5
    Post Likes

    TXV hot swap

    The company I work for pushes us to do hot swaps on 410 TXV's. I'm not a big fan of doing it this way. I'd like to get others' thoughts/pros/cons on doing this.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    What do you mean by 'hot swap'



  3. #3
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,711
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    What do you mean by 'hot swap'
    X2
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. #4
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,968
    Post Likes
    Twilly says they steal it from one house and install it in another and get paid for it.
    No Heat No Cool You need Action Fast

  5. #5
    Join Date
    Mar 2010
    Location
    Fayetteville, AR
    Posts
    5
    Post Likes
    Thread Starter
    Hot Swap is when we pump down the system into the condensor and leave some pressure in it so we are venting some of the 410A
    They tell us that it is faster this way and we dont have to test with nitrogen or pull it down in a vacuum.

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    Quote Originally Posted by Lawrence a View Post
    Hot Swap is when we pump down the system into the condensor and leave some pressure in it so we are venting some of the 410A
    They tell us that it is faster this way and we dont have to test with nitrogen or pull it down in a vacuum.
    I've done things this way and can say from experience that it is t a good method.

    Do I right.



  7. #7
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    If the txv is equiped with mechanical conections , such as chatleff with seals , then there is nothing wrong at all with changing the valve with say , 5 psi on the lines and evap.

    Residential speaking.

    This saves time , avoids contamination , and is perfectly do-able.

    New drier or evacuation not needed.

    Even with zero pounds , Carrier says vapor will still exit for some time , preventing air and moisture from entering. (you can see the fumes)

    Also , you can easily thumb a hole with five pounds.

  8. #8
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    3,063
    Post Likes
    I was taught that moisture can enter a system even with pressure on the system because moisture always runs from wet to dry. I think the term was vapor pressure can push moisture into a system through a leak even though the system never loses the total charge. I will admit to quickly changing a txv a time or two the way mentioned without any ill effects that I know of.

  9. #9
    Join Date
    Oct 2008
    Location
    Cleveland, Ohio
    Posts
    27
    Post Likes

    ???????

    Last time I checked 99% of us get paid by the hr. I recommend residential, commercial no matter what application pump it down, change the txv, change the drier and vac the system. This leaves little room for error. That's my personal opinion.

  10. #10
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,884
    Post Likes
    Quote Originally Posted by BobbyBJr View Post
    I was taught that moisture can enter a system even with pressure on the system because moisture always runs from wet to dry. I think the term was vapor pressure can push moisture into a system through a leak even though the system never loses the total charge. I will admit to quickly changing a txv a time or two the way mentioned without any ill effects that I know of.
    Are you saying moisture can travel from atmospheric pressure to a closed pressurized system through a leak???????? How is this possible???????

  11. #11
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    I've done hot swaps on large supermarket systems where pulling a 500 micron vacuum before all the food melts would be impossible and its worked fine.

    Ive hot swapped TXV thermal elements on commercial and residential systems many times with no trouble.

    I've never hot swapped a valve on a small split system though. The only ones I've changed required brazing and you can't do that on the fly.

    I've never seen a 410a expansion valve fail yet, knock on wood.

  12. #12
    Join Date
    Sep 2010
    Location
    Western, MO
    Posts
    988
    Post Likes
    What part of doing this worries you?

    Then we can answer that problem.

    jim
    Common sense isn't very common anymore.

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,244
    Post Likes
    This thread contains DIY info. It should not be in an open forum.

    JMHO.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.