    When taking a amp. reading to set your heat anticipator on a T87 should the t stat be in or out of the circut. I am looking a a diagram of the procedure and it is not clear where they are taking the reading.
    Is the setting for a Taco zone valve .9
    The obvious is obvious
    Florida
    All the stat is is a switch, so I'd just measure it either way as long as the units running. Don't know about the Taco valve.
    Apr 2004
    you would jump R and W at the thermostat. On a t87, you cant do that with the stat connected to the subbase.
    Taco zone valves generally were .9 last time I did one.
    Florida
    Can't you take your reading at the furnace with the stat on? Seems to me it doesn't matter as long as it's running and drawing control voltage....
    May 2005
    1- remove red stat wire from r termenal
    2-put one end of ten loop on r term
    3- put other end of ten loop on w term
    4- furnace should start now
    5-now measure amp draw
    6-this will be your anticipater setting
    7-AND HAVE A NICE DAY
    New Hampshire
    Set the heat anticipator at .9 then you're done.
    I never check the current draw and don't have problems with them.
    May 2005
    check with stat out of circuit or you will fry the stat
    I've set hundreds and never smoked a tstat. Please explain. Done with tstat in circuit and out.
    I asked because a diagram that I saw was confusing and I was unable to locate any specific information on the net. I would think that if you measured with the t-stat in the loop the heat anticipator which is a resistor would affect the amp draw.
    Nov 2005
    BAKERSFIELD CA.
    get rid of the t87 and put in a good digital stat you wont have to worry about the heat anticapator setting and youll have a more accurate reading on the room temp. But if your gonna keep it just jump R to W at the subbase and get the reading there if you jump it at the unit you may not get the correct reading do to the resistance of the wire to the subbase not being measured
    Nov 2005
    BAKERSFIELD CA.
    get rid of the t87 and put in a good digital stat you wont have to worry about the heat anticapator setting and youll have a more accurate reading on the room temp. But if your gonna keep it just jump R to W at the subbase and get the reading there if you jump it at the unit you may not get the correct reading do to the resistance of the wire to the subbase not being measured and you really dont need a ten rap just a good meter