    Quote Originally Posted by mcewans View Post
    I know this is residential, but is this single phase or 3-phase?
    I had a call last night, no cool: determined that the fan side of the dual run cap was "no bueno". I didn't have the required microfarads on board; so, I went back this morning, (Saturday) with a turbo 200 (all they had). Out of curiousity I looked in the main return box, and saw a 14 in. round dust spot, on the plenum insulation, that was not cut out in the installation.

  2. #22
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Confused

    Quote Originally Posted by timebuilder View Post
    The poster I referenced is Canadian.
    ok.

  3. #23
    Join Date
    Aug 2011
    Posts
    3
    Post Likes
    you need a minimum #6 wire for a 50-60 amp breaker---I never agreed with doing by the max size because the breaker does act as a fuse.... why would you be ok with the amps being that high to begin with? There is obviously an issuse going on with excess amp draw loose txv bulb, over charge, dirty condenser, lack of return airlow ect.

  4. #24
    Join Date
    Jan 2010
    Location
    Van Buren Arkansas
    Posts
    16
    Post Likes
    Thread Starter

    wire size

    Quote Originally Posted by Senator View Post
    you need a minimum #6 wire for a 50-60 amp breaker---I never agreed with doing by the max size because the breaker does act as a fuse.... why would you be ok with the amps being that high to begin with? There is obviously an issuse going on with excess amp draw loose txv bulb, over charge, dirty condenser, lack of return airlow ect.
    We called an electrician out for this customer. They ran #6 wire all the way to the unit. New 50 amp breaker, new disconnect, real fine job.

  5. #25
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    Unless you hire the electrician, you can't bill for him. How are you going to get paid for the whip if you didn't install it.
    Beware of advice given by some guy on the Internet.

  6. #26
    Join Date
    Jan 2010
    Location
    Van Buren Arkansas
    Posts
    16
    Post Likes
    Thread Starter

    wire size

    Quote Originally Posted by Milk man View Post
    Unless you hire the electrician, you can't bill for him. How are you going to get paid for the whip if you didn't install it.
    I hadn't thought of that. The electrician is a guy I know, and I just had the customer call him.

  7. #27
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by acts238 View Post
    We called an electrician out for this customer. They ran #6 wire all the way to the unit. New 50 amp breaker, new disconnect, real fine job.
    This is a REAL suggestion.

    Ask your electrician friend why he didn't wire the outdoor unit according to article 430 of the NEC.

    Please post his answer back here.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #28
    Join Date
    Jan 2010
    Location
    Van Buren Arkansas
    Posts
    16
    Post Likes
    Thread Starter

    wire size

    Quote Originally Posted by timebuilder View Post
    This is a REAL suggestion.

    Ask your electrician friend why he didn't wire the outdoor unit according to article 430 of the NEC.

    Please post his answer back here.
    which part of article 430 NEC, are we looking at.

  9. #29
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    If the unit ran fine for 10 years on the 30 amp breaker, I suspect something else is up.

    2 weeks ago i got a no A/C call.

    Found this
    12 year old 4 ton trane
    40 amp breaker
    8 awg wire throughout
    25 amp fuses in the disconnect (looked original)

    MCA 40 amps
    MOP 50 amps

    cleaned the extremely dirty condenser, installed 30 amp time delay fuses (biggest that would fit in that disconnect), and tested compressor ohms and amp draw.

    everything was good.

    Two days later the compressor shorted to ground.

    I suspect the compressor was on its way out and thats what blew the fuses the first time.

  10. #30
    Join Date
    Sep 2011
    Posts
    7
    Post Likes
    Quote Originally Posted by acts238 View Post
    When I discovered the 30 amp tripped breaker, and checked the nameplate on the 50 amp min. unit. I quickly realized, someone made a mistake.
    a 50amp is a #6 thhn,all day long

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •