    lead lag cycles

    Im having issues with the lead lag cycles block in AX. Does anyone know how to program the lead lag cycles so that an alarm will latch to a boolean constant? I want the end user to be able to see that there is an alarm and then have to manually reset it before the output can start again.

  2. #2
    Join Date
    Oct 2007
    Location
    Huntsville, AL
    Posts
    405
    You can tie a status demux to the feedback of the lead lag cycles, You can then tie the alarm output of the status demux to a BooleanWritable.


    Im like a mushroom, they keep me in the dark and feed me crap.

  3. #3
    Join Date
    Oct 2009
    Posts
    630
    Im not sure what you mean. Is there any way you can post a screen shot of your example?

  4. #4
    Join Date
    Oct 2007
    Location
    Huntsville, AL
    Posts
    405
    I told you a little wrong in my original post but I have attached a picture of how I do pump failures. My example is using LeadLagRuntime but essentially would be the exact same with LeadLagCycles.
    Attached Images Attached Images  


    Im like a mushroom, they keep me in the dark and feed me crap.