    2.5 Ton vs 3.0 Ton

    I have a 1100 square foot house(excluding the garage).
    We currently have a 2.5 ton unit. We are looking to replace our current unit which was installed in 1994 due to not cooling when it's 100 degrees outside.
    Contracters are differing on 2.5 and 3. units. Does it really matter?

  2. #2
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    1,058
    Post Likes

    Yes,

    it could matter. How often does it get 100 degrees in your area? If the system is oversized, it may not de-humidify properly. The important thing is not to size a system based on a few days of higher then normal temperatures.
    Last edited by gregp; 08-09-2011 at 10:51 AM. Reason: can't spell worth crap

  3. #3
    Join Date
    Oct 2004
    Location
    Palm Desert home, Bear Valley Springs home & Maui condo
    Posts
    4,126
    Post Likes
    Yes it does.

  4. #4
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    I live in Miami, Florida

  5. #5
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Cool

    Quote Originally Posted by Mary9921 View Post
    I have a 1100 square foot house(excluding the garage).
    We currently have a 2.5 ton unit. We are looking to replace our current unit which was installed in 1994 due to not cooling when it's 100 degrees outside.
    Contracters are differing on 2.5 and 3. units. Does it really matter?
    curious, on those 100 degree days, what temp, do you think the unit should get to, that would make you comfortable/happy? and on those 100 degree days what does your current system reach with the 2.5 ton unit?

  6. #6
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes

    Arrow Do the testing to get the data first, on which to base decision on...

    Miami, FL, 2.5% summer design 90-F dry bulb, 77-F wet bulb 56% relative humidity.
    That figures to be a high 120.69 grs moisture per lb of air.

    In that humid climate, a Home Energy Audit should be performed with a blower door test.
    After any retrofit work, a manual J ought to be performed.
    With that high a humidity, the Infiltration Rate must be kept as low as possible.

    The duct system must be examined & airflow tested before selecting a new condenser & matching indoor coil.

    From that data, you & your contractor select the best combination of equipment & components that will work best in your climate, with your home, the final duct system & those humidity control needs.

    Good Luck...

  7. #7
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,047
    Post Likes
    Quote Originally Posted by Mary9921 View Post
    I have a 1100 square foot house(excluding the garage).
    We currently have a 2.5 ton unit. We are looking to replace our current unit which was installed in 1994 due to not cooling when it's 100 degrees outside.
    Contracters are differing on 2.5 and 3. units. Does it really matter?
    Sorry, 3 tons is crazy for 1100 sq ft.

    If you really require that much cooling, fix the house and ductwork. Throwing larger equipment at the problem won't make it go away.

    Chances are that the ductwork isn't sufficient for the 1000 cfm a 2.5 ton unit needs to move, let alone 1200 cfm for 3 tons.

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    The duct system must be examined & airflow tested before selecting a new condenser & matching indoor coil.
    Chances are that the ductwork isn't sufficient for the 1000 cfm a 2.5 ton unit needs to move, let alone 1200 cfm for 3 tons.
    There's the answer.

  9. #9
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    As others have stated, make sure your insulation is top notch, infiltration is at a minimum, duct-work is tight.
    Then put in a 1.5 or 2 ton, depending on manual J.
    Even 2.5 ton, in 100 degree heat, for 1100 sq ft is crazy.
    Also as stated here by someone very wise - insulation is something you pay for whether you have it or not.
    I have a 1000 sq ft rental, well insulated, with a 32 year old 1.5 ton A/C.
    It performed wonderfully when we recently hit 99 degrees. Renter was never uncomfortable.
    Keep in mind, a smaller unit will run longer cycles, and therefore de-humidify very well, which is ideal for your climate. On the hottest days, it will run nearly non-stop. That is a good thing.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  10. #10
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    78 degrees is comfortable

  11. #11
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    We are having the electric company come in and perform a test on the ducts before we hire the contractor to install the unit.

    the outside model is:Bryant 126BNA03600/inside:FV4CNF003T00

  12. #12
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes

    Lightbulb

    Quote Originally Posted by Mary9921 View Post
    We are having the electric company come in and perform a test on the ducts before we hire the contractor to install the unit.

    the outside model is:Bryant 126BNA03600/inside:FV4CNF003T00
    That is only ONE piece of the total data needed... listen to what the professionals & others have suggested on your thread...

  13. #13
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Smile

    Quote Originally Posted by Mary9921 View Post
    78 degrees is comfortable
    so how low is your existing system bringing the tempature on a 100 degree day!

  14. #14
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    approximately 86 degrees

  15. #15
    Join Date
    Aug 2011
    Posts
    16
    Post Likes
    how cold is the air coming out?

  16. #16
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    778
    Post Likes
    Quote Originally Posted by amd View Post
    Sorry, 3 tons is crazy for 1100 sq ft.

    If you really require that much cooling, fix the house and ductwork. Throwing larger equipment at the problem won't make it go away.

    Chances are that the ductwork isn't sufficient for the 1000 cfm a 2.5 ton unit needs to move, let alone 1200 cfm for 3 tons.
    I live and work down here. And I have seen 3 ton units on 1000 sq. foot that would not cool. Depends on how old the house is. How much outside air infiltration there is. And yes y'all made good points about insulation and all. But most of the older homes down here have no insulation under the floors much less any in the exterior walls. As for duct work sizing, Good luck with that in older homes. Most of them don't have enough space in the attic to crawl in much less fitting the right size duct work in. Roofs down here where never meant to shed snow. Just water. Odds are the original duct work was designed for heat only, The payscale is so low down here most people can barely afford the system muchless new duct work. Another question you should ask is do they ever intend to close in the garage. More than likely they will find that the ductwork is to blame for the lack of cooling plus poorly insulated.

  17. #17
    Join Date
    Aug 2011
    Posts
    568
    Post Likes

    Hmm

    Quote Originally Posted by meoberry View Post
    I live and work down here. And I have seen 3 ton units on 1000 sq. foot that would not cool. Depends on how old the house is. How much outside air infiltration there is. And yes y'all made good points about insulation and all. But most of the older homes down here have no insulation under the floors much less any in the exterior walls. As for duct work sizing, Good luck with that in older homes. Most of them don't have enough space in the attic to crawl in much less fitting the right size duct work in. Roofs down here where never meant to shed snow. Just water. Odds are the original duct work was designed for heat only, The payscale is so low down here most people can barely afford the system muchless new duct work. Another question you should ask is do they ever intend to close in the garage. More than likely they will find that the ductwork is to blame for the lack of cooling plus poorly insulated.
    good post.

  18. #18
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes

    Lightbulb

    The preceding posts illustrate why it is very important.to have a Home Energy Efficiency Audit with blower door numbers; later with a Manual J heatgain Calc

    In FL.; is there any help available from Power Companies or other sources for the preceding work listed above?
    Are there any loans that can be paid back with the utility cost savings?


    It would important to use vapor barriers & also get the high humidity infiltration down to the minimum 0.35-Air Changes per Hour (ACH).

    If you size for long runtimes with the lowest airflow per tonnage for a colder evap-coil for better humidity control higher temps will work okay; they also said they are comfortable at 80-F.

    My advice; use large floor type fans to circulate the air & dress to keep cool; that is a much better cost-effective & comfort option than over-sizing an A/C on undersized heating duct systems that won't cool worth a hoot...

    Also, try making the Return Air filter area larger.
    http://www.udarrell.com/filters_type...lect_from.html

  19. #19
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    it's pretty cold coming out of the air vents

  20. #20
    Join Date
    Aug 2011
    Posts
    8
    Post Likes
    Thread Starter
    We have pretty good insulation in the ceiling...hubby put it in after hurricane Andrew. And the house was built in 1984. No insulation in the floor or exterior walls

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •