2.5 Ton vs 3.0 Ton
I have a 1100 square foot house(excluding the garage).
We currently have a 2.5 ton unit. We are looking to replace our current unit which was installed in 1994 due to not cooling when it's 100 degrees outside.
Contracters are differing on 2.5 and 3. units. Does it really matter?
-
08-09-2011, 10:46 AM #2
Yes,
it could matter. How often does it get 100 degrees in your area? If the system is oversized, it may not de-humidify properly. The important thing is not to size a system based on a few days of higher then normal temperatures.
Last edited by gregp; 08-09-2011 at 10:51 AM. Reason: can't spell worth crap
-
08-09-2011, 10:47 AM #3
Yes it does.
Always drink upstream from the herd
-
08-09-2011, 10:53 AM #4
Regular Guest
- Join Date
- Aug 2011
- Posts
- 8
I live in Miami, Florida
-
08-09-2011, 11:02 AM #5
banned reincarnate
- Join Date
- Aug 2011
- Posts
- 568
-
08-09-2011, 11:42 AM #6
Do the testing to get the data first, on which to base decision on...
Miami, FL, 2.5% summer design 90-F dry bulb, 77-F wet bulb 56% relative humidity.
That figures to be a high 120.69 grs moisture per lb of air.
In that humid climate, a Home Energy Audit should be performed with a blower door test.
After any retrofit work, a manual J ought to be performed.
With that high a humidity, the Infiltration Rate must be kept as low as possible.
The duct system must be examined & airflow tested before selecting a new condenser & matching indoor coil.
From that data, you & your contractor select the best combination of equipment & components that will work best in your climate, with your home, the final duct system & those humidity control needs.
Good Luck...AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
08-09-2011, 11:46 AM #7
Regular Guest
- Join Date
- Sep 2002
- Location
- I don't know
- Posts
- 2,888
Sorry, 3 tons is crazy for 1100 sq ft.
If you really require that much cooling, fix the house and ductwork. Throwing larger equipment at the problem won't make it go away.
Chances are that the ductwork isn't sufficient for the 1000 cfm a 2.5 ton unit needs to move, let alone 1200 cfm for 3 tons.
-
08-09-2011, 12:58 PM #8The duct system must be examined & airflow tested before selecting a new condenser & matching indoor coil.
There's the answer.Chances are that the ductwork isn't sufficient for the 1000 cfm a 2.5 ton unit needs to move, let alone 1200 cfm for 3 tons.
-
08-09-2011, 06:24 PM #9
As others have stated, make sure your insulation is top notch, infiltration is at a minimum, duct-work is tight.
Then put in a 1.5 or 2 ton, depending on manual J.
Even 2.5 ton, in 100 degree heat, for 1100 sq ft is crazy.
Also as stated here by someone very wise - insulation is something you pay for whether you have it or not.
I have a 1000 sq ft rental, well insulated, with a 32 year old 1.5 ton A/C.
It performed wonderfully when we recently hit 99 degrees. Renter was never uncomfortable.
Keep in mind, a smaller unit will run longer cycles, and therefore de-humidify very well, which is ideal for your climate. On the hottest days, it will run nearly non-stop. That is a good thing."Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler
-
08-09-2011, 07:34 PM #10
Regular Guest
- Join Date
- Aug 2011
- Posts
- 8
78 degrees is comfortable
-
08-09-2011, 07:39 PM #11
Regular Guest
- Join Date
- Aug 2011
- Posts
- 8
We are having the electric company come in and perform a test on the ducts before we hire the contractor to install the unit.
the outside model is:Bryant 126BNA03600/inside:FV4CNF003T00
-