Thread: txv problems

  1. #1

    txv problems

    so do txvs go bad after sometime. i had a service call on a 410a carrier system. suction pressure was low 60 psig. discharge pressure was 235 psig. I let the home owner know her txv was bad and changed it out ran the system in cooling and the ac was cooling.

  2. #2
    Join Date
    Feb 2011
    Location
    North East Ohio
    Posts
    772
    Its a mechanical device with moving parts in it. Yes they can go bad

  3. #3
    pressures sound low... did you leak check?

  4. #4
    The house is a track home 5 years old I checked the welds and found no oil staining so I don't think they were leaks

  5. #5
    once you replaced the txv, what was the subcooling? both pressures were pretty low for 410a

  6. #6
    Subcooling was 11 degrees and suction pressure was 165 and discharge pressure was 265

  7. #7
    Join Date
    Jan 2011
    Posts
    92
    Still seems strange. Head pressure seems low. With a suction that high you'd expect to see mid eightees inside. So I'm assuming it was hot out. Is the condenser shaded?