  1. #14
    Join Date
    Nov 2010
    Location
    Montreal, Quebec.
    Posts
    71
    Here is why I was asking, bare with me the post will be a little long however it makes for an interesting debate.

    Heat-loss calculated to 56,300 Btu at -14.8F (Montreal)
    Heat-gain calculated to 24284Btu at 86F (it's actually 19427 true gain they then add 25% for a HP)

    I am on dual rate electricity where I pay a low rate down to 10F and a high rate below that. My furnace is propane, my electric company puts in relay that switches my heat pump to my furnace at and below 10F.

    Low rate = 4.33 cents kw/h
    High rate = 18.14 cents kw/h
    Propane = 67 cents per litre or 9.44 cents per Kw/h

    Units that will be purchased are Carrier Infinity 25VNA (greenspeed) HP which can go down to 40% of max output and a 58MVC that goes down to also approx. 40% of max output (this will be imporatant further down)

    It is unlikely that if my heat-loss is 56,300Btu at -14.8F that it would be as little as 24284Btu at 10F when I switch over to propane. Therefore somewhere between say 32F and 10F my HP would need the furnace to help.

    At 17F my COP is 2.46, my furnace is 96.6% efficient so my rates are:

    electricity = 1.76 cents per Kw/h
    Propane = 9.77 cents per Kw/h

    You can see why I would like my HP to be able to handle the full load down to 10F. It makes no sense to spend all this money on ultra efficient equipment to throw it out the window because I use aux heat earlier than needed.

    The engineering company can't tell me what my heat-loss is at 10F for some reason however I believe it to be more than the 2T HP. Since the equipment I am buying is variable speed multistage I think it makes sense to move up to the 3T HP since it can go down to 40% of 36000 Btu or so for summer AC. The extra Ton should produce some good cost savings in winter. Keep in mind also that we only AC for about 2 weeks in summer. It would be nice to know the actual heat-loss at 10F however I am not sure I would be comfortable oversizing my HP by more than 1T if it were more than 36KBtu anyway.

    Comments / advice??

  2. #15
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,373

    Possible

    Quote Originally Posted by Norm01 View Post
    Here is why I was asking, bare with me the post will be a little long however it makes for an interesting debate.

    Heat-loss calculated to 56,300 Btu at -14.8F (Montreal)
    Heat-gain calculated to 24284Btu at 86F (it's actually 19427 true gain they then add 25% for a HP)

    I am on dual rate electricity where I pay a low rate down to 10F and a high rate below that. My furnace is propane, my electric company puts in relay that switches my heat pump to my furnace at and below 10F.

    Low rate = 4.33 cents kw/h
    High rate = 18.14 cents kw/h
    Propane = 67 cents per litre or 9.44 cents per Kw/h

    Units that will be purchased are Carrier Infinity 25VNA (greenspeed) HP which can go down to 40% of max output and a 58MVC that goes down to also approx. 40% of max output (this will be important further down)

    Comments / advice??

    Short answer:
    Yes, I would install 3 Ton 25vna, the first stage cooling would and should operate the majority of the time anyway. I would definitely install an 80,000 58mvc and a modulating plenum heater as a system package. The heatpump and plenum should be considered as one unit; working together.
    Let me be understood: this package is very common for us here with better rates, so, perhaps this system package might not be economical for you.

  3. #16
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,296

    Thumbs up Interpolation from 70F down to -15F

    Quote Originally Posted by Norm01 View Post
    Here is why I was asking, bare with me the post will be a little long however it makes for an interesting debate.

    Heat-loss calculated to 56,300 Btu at -14.8F (Montreal)
    Heat-gain calculated to 24284Btu at 86F (it's actually 19427 true gain they then add 25% for a HP)

    It is unlikely that if my heat-loss is 56,300Btu at -14.8F that it would be as little as 24284Btu at 10F when I switch over to propane. Therefore somewhere between say 32F and 10F my HP would need the furnace to help.

    At 17F my COP is 2.46, my furnace is 96.6% efficient so my rates are:

    electricity = 1.76 cents per Kw/h
    Propane = 9.77 cents per Kw/h

    You can see why I would like my HP to be able to handle the full load down to 10F.

    The engineering company can't tell me what my heat-loss is at 10F for some reason however I believe it to be more than the 2T HP.

    Since the equipment I am buying is variable speed multistage I think it makes sense to move up to the 3T HP since it can go down to 40% of 36000 Btu or so for summer AC.

    The extra Ton should produce some good cost savings in winter. Keep in mind also that we only AC for about 2 weeks in summer.

    It would be nice to know the actual heat-loss at 10F however I am not sure I would be comfortable oversizing my HP by more than 1T if it were more than 36KBtu anyway.

    Comments / advice??
    At 15'F heat load is ~ 36,000 BTU/hr

    -15 56,300 85
    -10 52,988 662
    -5 49,676 3312
    0 46,365
    5 43,053
    10 39,741
    15 36,429
    20 33,118
    25 29,806
    30 26,494
    35 23,182
    40 19,871
    45 16,559
    50 13,247
    55 9,935
    60 6,624
    65 3,312
    70 0
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  4. #17
    Join Date
    Nov 2010
    Location
    Montreal, Quebec.
    Posts
    71
    Quote Originally Posted by dan sw fl View Post
    At 15'F heat load is ~ 36,000 BTU/hr

    -15 56,300 85
    -10 52,988 662
    -5 49,676 3312
    0 46,365
    5 43,053
    10 39,741
    15 36,429
    20 33,118
    25 29,806
    30 26,494
    35 23,182
    40 19,871
    45 16,559
    50 13,247
    55 9,935
    60 6,624
    65 3,312
    70 0
    Thank you sir

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event