    Question TROUBLESHOOTING TRANE XE-1000

    Am novice, having taken training and getting EPA certified, and would appreciate any advice you can give.

    Am troubleshooting a relative's system (seemed like good experience). Trane Model TWR042C100B3.

    Unit was freezing. Troubleshooting guides in training books indicated low refrigerant. (Low Discharge Presssure; Low Suction Pressure; High superheat; Low subcooling)

    However, system would not charge to proper discharge pressure--could only get it to around 240 at 98-100 ambient, and suction pressure has raised to around 78. Superheat has improved, but remains high; subcooling has improved to within normal parameters.

    Am believing the compressor is the culprit. However, amps are drawing at 17-17.5 on a 19 amp rated motor.

    Is that difference significant enough to point toward compressor weakness?

    Thanks.

    Also, how can I tell if I overcharged this sytem while attempting to get the discharge pressure up?

  2. #2
    Join Date
    Aug 2011
    Posts
    568

    Confused

    Quote Originally Posted by lbg8994 View Post
    Am novice, having taken training and getting EPA certified, and would appreciate any advice you can give.

    Am troubleshooting a relative's system (seemed like good experience). Trane Model TWR042C100B3.

    Unit was freezing. Troubleshooting guides in training books indicated low refrigerant. (Low Discharge Presssure; Low Suction Pressure; High superheat; Low subcooling)

    However, system would not charge to proper discharge pressure--could only get it to around 240 at 98-100 ambient, and suction pressure has raised to around 78. Superheat has improved, but remains high; subcooling has improved to within normal parameters.

    Am believing the compressor is the culprit. However, amps are drawing at 17-17.5 on a 19 amp rated motor.

    Is that difference significant enough to point toward compressor weakness?

    Thanks.

    Also, how can I tell if I overcharged this sytem while attempting to get the discharge pressure up?
    answer to all your troubles, call a qualified hvac tech, good luck!

  3. #3
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,896
    Twilly says this really falls under DIY. Superheat to you and yours.
    No Heat No Cool You need Action Fast

  4. #4
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,512
    alot of the old tranes were a piston metering device

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event