    York YT Average purge time?

    I am working on a York YT R123 Machine. I new it had a leak, so I pulled all the refrigerant. Perfomed a leak search. Found the leak in the releif. Replaced the relief. Evacuated the system, charged it back up. Now I have a portale purge unit on it. Should I leave the purge unit on all night? Or is there a formula to calculate how long to leave it on? There is 810 lbs in the system.

  2. #2
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    No known formula for the time it takes a purge to remove whatever non-condenseables from a system, Far too many variables.
    As for leaving a purge on unattended, well....that my friend is truly a crap-shoot.
    Assuming your purge has some type of float to return condensed refrigerant, should it hang up and not open, it would be very easy for your purge to dump 400-500 pounds of refrigerant overnight.(Don't ask me how I know this)
    Personnaly...I would not even get a cup of coffee and leave a portable purge pumping unattended.
    Ain't "None" of us as smart as "All" of us..

  3. #3
    Join Date
    Aug 2011
    Location
    Tucson, AZ
    Posts
    7
    Quote Originally Posted by RichardL View Post
    No known formula for the time it takes a purge to remove whatever non-condenseables from a system, Far too many variables.
    As for leaving a purge on unattended, well....that my friend is truly a crap-shoot.
    Assuming your purge has some type of float to return condensed refrigerant, should it hang up and not open, it would be very easy for your purge to dump 400-500 pounds of refrigerant overnight.(Don't ask me how I know this)
    Personnaly...I would not even get a cup of coffee and leave a portable purge pumping unattended.
    Agreed, I guess I already new the answer to my question. Just really tired and trying to get this machine online.

  4. #4
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,611
    If you evacuated the machine before recharging, what's the reason for having a portable purge hooked up? Start it up and let the unit mounted purge take care of the residual n/c's.

  5. #5
    Join Date
    Jun 2010
    Location
    Tampa, FL
    Posts
    101
    It would have been a better idea to use the portable purge on the recovery tank. Never had that much air from recovery tank to cause surge. If head goes a little high on start-up, keep vanes closed until onboard purge removes air.

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,110
    I agree with the other previous posters ....but why not really solve your problem and scrap the POS York refrigerant guzzler purge and put a Trane purifier on it ???
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  7. #7
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,611
    Quote Originally Posted by graham View Post
    I agree with the other previous posters ....but why not really solve your problem and scrap the POS York refrigerant guzzler purge and put a Trane purifier on it ???
    He apparently solved his problem by fixing the leak.

    It's always been my philosophy that people tend to run things down simply because they don't understand them. Other than the fact that it doesn't work during the off cycle (which is admittedly a downside), the turboguard purge is a very good system. Been around for years, don't give a ton of trouble, just works. Can't ask for much more than that....

  8. #8
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,110
    Quote Originally Posted by klove View Post

    (which is admittedly a downside), Can't ask for much more than that....
    I would ask that it does run during the off cycle and doesnt guzzle refrigerant . And i do understand how the Turboguard works .
    !!!!
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  9. #9
    Join Date
    May 2011
    Location
    Gateway to the west
    Posts
    21
    If your chiller is leaking so much that your purge needs to run in the
    "OFF CYCLE" wouldn't it just be better to fix the leaks?

  10. #10
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Quote Originally Posted by graham View Post
    I agree with the other previous posters ....but why not really solve your problem and scrap the POS York refrigerant guzzler purge and put a Trane purifier on it ???
    I just installed a purifier purge on 2 YT's. Not only do they look good they work great to.

  11. #11
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,110
    Quote Originally Posted by Phisher View Post
    I just installed a purifier purge on 2 YT's. Not only do they look good they work great to.
    I rest my case
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  12. #12
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,611
    Quote Originally Posted by graham View Post
    I rest my case
    No need to rest your case - I've installed purifiers and skyguards on all sorts of low pressure machines. They do work well. But that doesn't mean the turboguard isn't a good design or that it doesn't work well - it's simply different. If you'd like we can talk about why the purifiers had to have a maximum pumpout timer incorporated into their design (they ain't perfect, either). I don't recall one of those "refrigerant guzzler" turboguards ever pumping a couple thousand pounds of refrigerant into the floor......

  13. #13
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    880

    Purifier Purge

    I have to go along with other tech's about this thread. If you evacuated the chiller to a proper level prior to putting the charge back in and get the air out of your recovery system hoses, your purge requirements should be almost 0. Unless your recovery system has a problem. While I agree York's purge maybe decent, Trane's is a lot better as long as the heat exchanger canister remains clean. If the machine has a moisture problem then it doesn't take long for the exchanger to become fouled. But then again if you have moisture in the chiller, no purge will help. As seen by the vice-president in charge of looking through the window (ie) sightglass. Anyway my vote goes to Trane.-Geo
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event