    I got a call from a friend tonight. He said he came home to a cold house and his carrier furnace baord was flashing 1 long and 3 short (or maybe 3 shorts and 1 long) He turned off the power and turned back on , and then it ignited and run normal until the stat was satisfied. He says there is nothing on or inside the cover telling what the code means. I work on Tranes everyday and dont have the Carrier fault codes in my head. Can someone tell me what to check if it does it again .
    Thanks
    Randy

  2. #2
    Join Date
    Aug 2002
    Posts
    490
    I don't have the code either, but check the pressure switch may be going or line clogged.
    also you can check the flame sensor to may have to clean it off.
    hope this helped

  3. #3
    Join Date
    Aug 2005
    Location
    Lafayette, IN
    Posts
    63
    i believe a 13 is an open high limit or flame roll out and a 31 is an ignition failure lockout, but i may be wrong.

  4. #4
    Join Date
    Jun 2005
    Posts
    178
    check the filter and the return air and make sure they are not blocked by furniture or covered by somthing if they are in the floor.filter may be clogged or even the coil if it has ac.

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    17,840
    13= Limit switch lockout.
    31= High pressure switch fault.
    "Politicians are the lowest form of life on Earth. Liberal Democrats are the lowest form of politician"

    - General George S. Patton

  6. #6
    Join Date
    Jun 2005
    Posts
    178
    is it a high efficiancy unit if so could be blocked trap if it went out on pressure sw.

  7. #7
    Join Date
    Jun 2005
    Posts
    178
    how old is unit and how long has it been running in home.

  8. #8
    Join Date
    Feb 2004
    Location
    KY
    Posts
    108
    I dont have the model # , I do know its an 80% Carrier about 10 years old.
    Im sure it didnt "fix "itself so the problem will come back and I will have to go over there.
    Thanks Guys

  9. #9
    Join Date
    Nov 2005
    Location
    detroit mi
    Posts
    4
    long flash=1rst digit
    shorter flash=2nd digit
    13=hi limit
    31=ignition failure

  10. #10
    Join Date
    Jul 2005
    Posts
    12
    So what is a High limit and what do you do to remedy the problem?

  11. #11
    Join Date
    Jan 2003
    Location
    Kentucky
    Posts
    2,651

    Thumbs up

    have a company in your area come and check it out for you...easiest and safest way to go

  12. #12
    Join Date
    Jul 2005
    Posts
    12
    Per a Google search, High limit fault: Temperatures in heat exchanger too high. High limit signaled/tripped. Air flow might be reduced/restricted such as a very dirty air filter to cause such problem.
    Found it. And yes, if Air filter is found to be ok, then a call to a qualified HVAC Tech would be in order.


    [Edited by dro1984 on 11-15-2005 at 07:41 PM]

  13. #13
    Join Date
    Nov 2001
    Location
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    Posts
    2,412
    Originally posted by big ern
    long flash=1rst digit
    shorter flash=2nd digit
    13=hi limit
    31=ignition failure
    Too much beer there ern.

    short flashes first digit,
    long flashes second digit.
    I love my job, but paydays Thursday

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event