Results 1 to 13 of 13
    KY
    Question
    I got a call from a friend tonight. He said he came home to a cold house and his carrier furnace baord was flashing 1 long and 3 short (or maybe 3 shorts and 1 long) He turned off the power and turned back on , and then it ignited and run normal until the stat was satisfied. He says there is nothing on or inside the cover telling what the code means. I work on Tranes everyday and dont have the Carrier fault codes in my head. Can someone tell me what to check if it does it again .
    Randy
    I don't have the code either, but check the pressure switch may be going or line clogged.
    also you can check the flame sensor to may have to clean it off.
    hope this helped
    Aug 2005
    Attica, IN
    i believe a 13 is an open high limit or flame roll out and a 31 is an ignition failure lockout, but i may be wrong.
    check the filter and the return air and make sure they are not blocked by furniture or covered by somthing if they are in the floor.filter may be clogged or even the coil if it has ac.
    SE Michigan
    13= Limit switch lockout.
    31= High pressure switch fault.
    "If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding
    is it a high efficiancy unit if so could be blocked trap if it went out on pressure sw.
    how old is unit and how long has it been running in home.
    KY
    I dont have the model # , I do know its an 80% Carrier about 10 years old.
    Im sure it didnt "fix "itself so the problem will come back and I will have to go over there.
    Thanks Guys
    Nov 2005
    detroit mi
    long flash=1rst digit
    shorter flash=2nd digit
    13=hi limit
    31=ignition failure
    Jul 2005
    So what is a High limit and what do you do to remedy the problem?
    Jan 2003
    Kentucky
    Thumbs up
    have a company in your area come and check it out for you...easiest and safest way to go
    Jul 2005
    Per a Google search, High limit fault: Temperatures in heat exchanger too high. High limit signaled/tripped. Air flow might be reduced/restricted such as a very dirty air filter to cause such problem.
    Found it. And yes, if Air filter is found to be ok, then a call to a qualified HVAC Tech would be in order.
    [Edited by dro1984 on 11-15-2005 at 07:41 PM]
    Nov 2001
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    13=hi limit
    31=ignition failure
    Too much beer there ern.
    short flashes first digit,
    long flashes second digit.
    I love my job, but paydays Thursday